Can a pendent ESFR sprinkler be installed directly on a welded outlet of a 4-inch branch pipe?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
9/8/2022 07:22:25 am
Yep, no issues as long as the deflector stays within its min/max distances.
Reply
Glenn Berger
9/8/2022 08:16:00 am
Dan nailed the issue. Location of the deflector with respect to the ceiling or roof as applicable.
Reply
Alex
9/8/2022 08:18:50 am
As Dan mentioned, no issues as long as you stay within the requirements outlined in NFPA 13 (2019) Chapter 14 Installation Requirements for Early Suppression Fast-Response Sprinklers.
Reply
Casey Milhorn
9/8/2022 08:44:54 am
As others have said, no issue other than deflector distance. We had a job many moons ago, where it made more sense to use 4" branch lines and ESFRs than a fire pump. Basically it was an existing building, with multiple lead-ins that were technically each coming off of a semi-public water main (one of those installed back before public vs private demarcation was really worried about). Long story short, 4" branches with ESFRs had to be used. Due to some sagging structure and wind bracing we had to really jam the pipe up tight to get the deflector distance correct. Not as bad as the old days of sch. 40 6" and 8", but it was a draining install for the guys in the field.
Reply
Jesse
9/8/2022 08:53:14 am
Yep. Just make sure the deflector is within the minimum and maximum distances required by its listing.
Reply
S
9/8/2022 08:55:42 am
Is this possibly a typo and you were asking about an Upright and not a Pendent? With an Upright your answer is no.
Reply
Fernando
9/8/2022 09:33:10 am
Maybe
Reply
Jon Griffin
9/8/2022 09:15:03 am
"S",
Reply
Franck
9/9/2022 09:17:39 am
Fully agree
Reply
David Kendrick
9/8/2022 10:36:38 am
Well said.
Reply
Mike
9/8/2022 02:52:10 pm
Agreed
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |