Should return air duct smoke detectors associated with a fan system close only the associated damper and shutdown the fan or close all dampers on the system (including supply return spill and outside air)?
How should outside air and spill air fire smoke dampers be controlled? Should these to be controlled by fire alarm? Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Jonathan Sullivan
7/8/2020 10:22:54 am
It depends. I think we need more information to help you. Is this equipment part of an engineered smoke control system, what type of fire alarm system do you have, is there a fire command center with damper control, etc.
Reply
Manny Rios
7/8/2020 10:25:35 am
In our jurisdiction and in compliance with applicable code requirements, (Mechanical and NFPA72) the hvac systems are designed with all devices connected to the fire alarm.
Reply
Scott McCormick
7/8/2020 10:50:09 am
Duct detectors are the MOST misused fire alarm device. I've seen more duct detectors installed that weren't required in the first place. People don't understand what the purpose of the detector. Perfect example, Lowes, Home Depot, Walmart, BJ's etc. large RTU with minimal duct work. Bam duct detector. Why? Where is the smoke going? I've had more Engineers and contractors say, "it's more than 2000 CFM." my answer is, So! Again I ask, Where is the smoke going to go? I have done a lot of research, and I understand the purpose. Read the documents about the MGM fire, La Vegas 11/21/1980 most of the 85 dead, died of smoke inhalation. When connected to a fire alarm system, these should be supervisory only.
Reply
Bruce Verhei
7/10/2020 08:01:57 pm
The essentially no duct HVAC units at ceiling-roof level have been at top of Tomes Van Rickley & Assoc., then TVA, then Telgian’s Pre-app meeting building department checklist for twenty-five years. I believe by now they’ve managed to have the requirement explicitly not required any more in the IMC.
Reply
Chris D
7/8/2020 11:46:21 am
Duct detectors typically shut down the entire HVAC system they are associated to but not all systems in the building.
Reply
Glenn Berger
7/8/2020 12:21:13 pm
There is no one right answer. It all depends on the geometry of the facility being protected and the arrangement of the HVAC System.
Reply
MHK
7/21/2020 02:46:09 am
I have looked at 6.4.3.1 of NFPA 90A (2018 ed.) and found that duct smoke detectors are only to stop their respective fan(s). Am I geeting anything wrong here?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |