I have a Business occupancy building that is being remodeled and new RTUs units are being installed.
There was a mechanical inspection done recently and the inspector is asking for duct smoke detectors on the supply-side of units under 2,000 CFM. The units supply air to common areas to a single floor and don’t physically share ducts or plenums. There is no smoke detector coverage since it’s a sprinklered building. We do have smoke detectors above fire alarm equipment are required. I tried searching for an answer in IBC, IFC, and NFPA standards, but couldn’t find a definite answer. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
5/17/2023 07:58:35 am
Not a FA guy however this chart comes to mind...
Reply
Dan Wilder
5/17/2023 08:01:17 am
Check the comments for some additional requirements from the original post as well, maybe there is some confusion on what is being asked...
Reply
Ira Matthews
5/17/2023 07:59:49 am
The requirements for duct smoke detection are found in section 606 of the 2018 International Mechanical Code. 606.2.1 has an exception that does not require duct detection in units that equal to or less than 2,000 CFM.
Reply
Jesse
5/17/2023 08:07:36 am
Did he provide a code reference?
Reply
Scott McCormick
5/17/2023 08:16:12 am
Duct detectors are the most common device installed wrong 98% of the time. I would ask the Enforcement Agency for a Code Section.
Reply
SCHULMAN
5/17/2023 08:40:14 am
I would contact the design team (Mechanical Engineer and Architect) and get a read on the Life Safety approach to the design - they may be using an obscure exception in the code that could trigger the requirement. I've not gotten anywhere asking Inspectors to provide me with code references ...
Reply
Fire Inspector AHJ
5/17/2023 09:46:48 am
They are requiring it because it is a shared space with over 2,000 CFM. The smaller units combined, feeding one space, would trigger a global shut down of all of the units at once.
Reply