Would a dry fire suppression system be affected by freezing temperatures?
I work at a facility that had a glass sprinkler break, no contact or anything, and of course the water came out as it should. We've had freezing temps for the last few days, but where it broke was in an 74 degree room, so not frozen. Any ideas on why this would have happened? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
2/1/2024 06:47:21 am
The room is 74 degrees but is fed from a dry sprinkler system?
Reply
Dan Wilder
2/1/2024 08:20:43 am
I'll add - was the room unheated until recently?
Reply
Anthony
2/1/2024 07:54:38 am
With out knowing more it could be a case where the bulb broke a while back and never fully let go. A slight nock that cracked the bulb but no one noticed the bubble wasn't there. A surge in pressure in the system or a rattle in the building that made its way to the pipes ended up shaking the bulb loose letting the sprinkler go off.
Reply
Franck
2/1/2024 09:18:58 am
As indicated above, the most obvious possible reason is related to the installation of the sprinkler with some damages (undetected until the issue happens).
Reply
Jesse
2/1/2024 11:17:35 am
I'm curious about the dry-system protecting a 74-degre room. Regardless, the sprinkler could have been damaged (likely) or defective (less likely).
Reply
Todd E Wyatt
2/1/2024 11:41:16 am
Some of the responses allude to possible past damage to the sprinkler's glass bulb heat-responsive element.
Reply
Dan S.
2/1/2024 05:14:43 pm
I bet you had water accumulation above sprinkler head in un heated area/attic that froze then thawed pushing out element. A lot of times the weakest link breaks first.
Reply
Chris
2/8/2024 09:11:07 am
What I have personally seen happen is the pipe will have water in it that freezes and as that water expands it will push out the sprinkler sealing assembly out of the sprinkler head but since the pipe is frozen solid it will stay sealed up until it eventually starts to thaw out. Then once it starts leaking air and the compressor starts running, it'll thaw out quickly as the air from the compressor gets hot and then the system trips. Years ago I went to fix a leak at a retirement facility because a head was leaking from it breaking from the freezing temp, when I got in the attic found that the head supplied the leaking dry SSP and then SSU's in the attic, the dry SSP was what had been leaking but every single SSU down the line was also broken but the orifices were still sealed up from the ice plugs so they hadn't leaked, and even cooler was a gasket on a mechanical tee was pushed out of its groove from an ice plug.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |