Does a double wall diesel tank require a reservoir?
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Dan Wilder
4/21/2023 08:16:31 am
Not specifically.
Reply
Dan Wilder
4/21/2023 11:48:03 am
and as I read the other comments leading towards containment not additional fuel storage...ugh TGIF!
Reply
James Phifer
4/21/2023 08:25:57 am
NFPA 20 2016 ed. 11.4.1.4.4 - Single-wall fuel tanks shall be enclosed with a wall, curb, or dike sufficient to hold the entire capacity of the tank.
Reply
Franck
4/21/2023 08:39:45 am
Normally not
Reply
Jesse
4/21/2023 08:51:35 am
Typically a twin-hulled diesel tank does not require secondary containment
Reply
4/21/2023 08:57:27 am
I would recommend to contact your state Environmental office for their requirements that may superceed some other code requirements from NFPA or local codes
Reply
Todd E Wyatt
4/21/2023 09:11:26 am
“Spill Control and Secondary Containment” for containers and tanks storing flammable and combustible liquids is addressed in the International Fire Code (IFC).
Reply
Sunil Kumar
4/21/2023 09:33:41 am
Not Really..
Reply
Connor
4/21/2023 10:08:03 am
This is a case where local environmental regulations will most likely govern. Most above-ground tanks containing petroleum products are subject to containment requirements, and whether or not the double wall counts as containment may depend on whether you have certain features like leak detection in the interstitial space, fill level sensing, etc.
Reply
If your project is with FM Global insurance , you need the double wall tank and a curb, or dike sufficient to hold the entire capacity of the tank plus one or two inches. I have seen this requirement in some specifications but is not a requirement from NFPA 20 or the local AHJ.
Reply
Panos
4/21/2023 02:01:56 pm
I once asked the FM Global guy why they require both double wall and a spill containment curbing for steel fire pump tanks.
Reply
Zack H
4/24/2023 12:29:51 pm
Thank you for this extra information. When I asked FM the same question, I got crickets in return, but I can unfortunately see that happening.
Sean Andrew Fallows
4/21/2023 01:40:29 pm
no. the second wall acts as the containment.
Reply
That depends upon the local codes. Double walled fuel oil tanks normally do not need any tertiary containment. The location of the tank (underground or above grade, lowest floor or upper floor of a building, etc) For diesel installations, a small day tank, installed locally, receives fuel from the main storage tanks (in NY the day tank is limited to a maximum volume of 275 gallons) .
Reply
MICHELE RIVAROLA
4/26/2023 10:57:09 am
Double walled tanks do not require additional containment but they require a drain and a leak detector
Reply
Phil Watkins
4/30/2023 03:46:31 am
Would depend on local environmental regulations which I would expect to supersede NFPA codes.
Reply