We are doing a design for high-piled storage of Class I-IV commodities in a palletized arrangement. Storage is 15'-6" high. Would this storage (image below) also count/qualify as "encapsulated" under NFPA 13 (2013 Edition)? The client is a remediation company that uses heavy plywood crates to temporarily store items for their clients (which are common household items).
Section 3.9.1.12 includes "a combustible package" as a method of encapsulation, but annex A.3.9.1.12 says "The term encapsulated does not apply to plastic-enclosed products or packages inside a large, non-plastic, enclosed container.". Does a heavy plywood crate count as encapsulation, or not? This matters because at 15.5 feet in height I would have to use the flow densities from 14.2.5 instead of the reduced ones from 14.2.4 if it does. Thanks very much for your help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
11/7/2023 06:56:00 am
It doesn't count as encapsulation. From NFPA 13 (2013 edition)
Reply
JI
11/7/2023 08:15:29 am
This is the way I read it as well. The "combustible packaging" refers to what is being encapsulated, and does not describe another type of encapsulation.
Reply
Alex
11/7/2023 08:31:53 am
I agree with Pete here! Not much more to add.
Reply
Jesse
11/7/2023 08:18:17 am
That's not encapsulated. Encapsulation typically uses a polystyrene or similar wrap on 5 sides of the load.
Reply
Nick
11/7/2023 08:29:39 am
I would be careful of following the commodity classifications found in chapter 5.6 of NFPA 13. See Table A.5.6 for examples of commodities not addressed by NFPA 13. It specifically lists "Storage Container - Large container storage of household goods" as not being addressed which I believe is the exact condition you show here.
Reply
Glenn Berger
11/7/2023 08:54:54 am
This is a classic case of utilizing the definitions from the standard being questioned.
Reply
Casey Milhorn
11/7/2023 09:17:27 am
Nick is spot on. This storage arrangement is becoming very popular with the self storage/moving companies. The customer can pack whatever they want in there while it sits in their driveway, close the door on it, have it picked up and stored two or three containers high in a warehouse that many times was never designed for this. I did a little research a few months back and I could not find any testing that has been done on this type of storage (I didn't spend a whole lot of time on it either). It definitely should be performance based design with someone experienced with this type of storage. It could test out very well in fire testing and be protected with OH2, then again it might need 2000gpm+ of ESFR protection, or not even allowed at all in certain arrangements. I would imagine the performance based spec would also dictate spacing of containers, flue spaces, aisles, max# of containers that can be stacked, clearance to roof sprinklers, etc.... just my two cents
Reply
OP
11/7/2023 09:29:15 am
Thanks everyone! I was leaning that way too but I wanted a few extra sets of eyes on it first.
Reply
Dan Wilder
11/7/2023 11:16:02 am
Encapsulation - I look at it as the ability to not allow prewetting of the pallet load (sides AND top) mostly with the use of plastic wrapping.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |