We have a stand alone open-air pool pavilion with no attached building.
There is a gas grill under the roof with a very elaborate hood/exhaust/Ansul system. There is no fire alarm system in this pool pavilion. The Fire Inspector wants the Ansul system monitored by the clubhouse fire alarm system that is 100-ft away. Is he correct by code? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
11/14/2022 08:13:10 am
You have a very unique case with a fire system provided for an outdoor exhaust system.
Reply
Jesse
11/14/2022 08:17:56 am
I agree with Glenn - this is a very unique situation. I think you can make the case to omit connection to the FA system, but as always it comes down to local AHJ requirements. Did the inspector provide a code reference?
Reply
Derek Crumley
11/15/2022 07:43:27 am
The inspector did not reference a code. After further conversation with AHJ they deem the pavilion to be attached to the clubhouse building because it is encompassed with in the pool fence that is attached to the clubhouse and wraps around pool and pool pavilion structure.
Reply
Alex
11/14/2022 08:18:36 am
Hi,
Reply
Todd Wyatt
11/14/2022 08:36:50 am
The adopted Fire Code (e.g. 2021 IBC) is the scoping document as to WHERE an “alternative” automatic fire-extinguishing system is permitted or required. The referenced standard (e.g. NFPA 96 Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations) identifies HOW the an “alternative” automatic fire-extinguishing system is to be designed, installed, inspected, and maintained.
Reply
Wes
11/15/2022 07:49:11 am
Just as a fallback, Potter just came out with a new wireless supervisory switch. If you had to connect it back to the main fire alarm system, at least you wouldn't have to dig and bury conduit to do so:
Reply
Frank J. Herrick
11/16/2022 11:24:29 am
In that situation I'd be happy with a 10" exterior bell and rated outdoor strobe.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |