Does a fire pump on an NFPA 13D system require backup power?
It seems like it should, but 13D does not say that it has to and does not reference NFPA 20. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Alex
4/6/2023 07:09:34 am
You are correct that NFPA 13D does not explicitly require backup power for fire pumps. NFPA 13D is primarily focused on life safety and providing occupants with enough time to evacuate in the event of a fire.
Reply
Chad
4/6/2023 08:06:33 am
As Alex said, that's a no redundant power. 13D is meant to be a cheap as reasonable to get as many homes protected as possible.... the pump doesn't need to even be listed for fire service. But of course there could be a good reason to require a more stringent system.
Reply
Wes
4/6/2023 08:40:29 am
I agree with the sentiment, but it's also a risk decision. We make an infinite amount of risk decisions when dealing with life safety and property protection systems everyday.
Reply
Jesse
4/6/2023 08:12:47 am
13D does not. 13D system pumps aren't necessarily NFPA 20 compliant. And NFPA 20 only requires backup power for pumps protecting high-rise buildings as long as the electrical supply is deemed reliable.
Reply
Dan
4/6/2023 08:15:59 am
No backup power for 13D. Would be reasonable to recommend where you believe the power may not be reliable. Same for commercial systems. Appendix of NFPA 20 gives guidance on what is considered ‘reliable’. You’ll see many, many systems using electric pumps and tanks (including breaks) without backup power. The key being reliability of power provision.
Reply
Bob Kleinheinz
4/6/2023 08:34:22 am
Very simple, NO 13-D is a Life Safety system and nothing more. The system is supposed to be a much less costly system and one that does not need maintenance, so we keep the cost and requirements down so the homeowners can afford the systems and we don't have to fight the home builders.
Reply
Todd E Wyatt
4/6/2023 08:56:12 am
SUMMARY
Reply
Todd E Wyatt
4/6/2023 08:56:36 am
REFERENCES
Reply
Todd E Wyatt
4/6/2023 09:01:08 am
REFERENCES continued ...
Reply
Todd E Wyatt
4/6/2023 09:01:52 am
REFERENCES continued ...
Reply
Anthony
4/6/2023 09:16:27 am
It does not. The requirements of NFPA 20 do not apply and the pumps do not need to be listed for fire protection. Per 13d-16 5.1.2.1.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |