I was looking through the International Building Code and have not found a requirement for a fire sprinkler riser room to be enclosed by a fire-rated wall.
Are there any requirements other than clearances to service the equipment for this room? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Randy
12/14/2020 11:18:52 am
Check NFPA 20 for equipment protection if you have a fire pump.
Reply
Jess L.
12/14/2020 11:47:26 am
Re: the Fire Pump Room, CA building code (IBC) calls it out in section 913.
Reply
Franck
12/14/2020 12:01:30 pm
If I speak as an AHJ, I would say : the more, the better...
Reply
Michael Major
12/14/2020 12:40:11 pm
Here in California, CFC 901.4.6 has requirements for the riser room size, what is allowed in the riser room, signs, access, lighting, and working space. Looks like it is model code, so should be in the IFC.
Reply
Todd E Wyatt
12/14/2020 01:13:14 pm
The 2021 IBC includes requirements for "riser rooms" per Section 902 including size, access, environment, and lighting but not a fire-resistance rating (FRR) for the walls for this room type.
Reply
Jonathan Joseph
12/14/2020 01:47:08 pm
I believe you would have to maintain the structure's exterior or interior fire rating for walls and ceilings depending on where it is located and what occupancies that are attached and surround the room.
Reply
John M
12/14/2020 07:48:51 pm
I am an AHJ. There is some language in NFPA 72 regarding smoke barriers and protection of the alarm components.
Reply
Mitchell O
12/14/2020 09:57:05 pm
Check NFPA 24 (2019) Section 6.2.9. This is section does have a requirement for the control valve to be located in a fire-rated room accessible from the exterior. There are 7 different options listed, any of which you can comply with. Here in Alaska, we don't use many PIVs nor do we located BFP outside (apparently it gets cold here), so this leaves us with few options beside rating the riser room. Local Gov't FPE's enforce this on every project.
Reply
sean
12/15/2020 07:03:45 am
you have not recieved a good answer. Not withstanding any local amendments the IBC/IFC only require rated construction around a fire pump room.
Reply
Franck
12/15/2020 11:45:35 am
Sean is right
Reply
Mitchell O
12/15/2020 07:49:52 pm
I agree with you Franck, that NFPA 13 starts at the valve on the riser (if one exists). In our case, our control valve (typically on the BFP) is located adjacent to the riser, in the same room.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |