I'm dealing with a commercial occupancy being a combination of large and smaller shops where automatic sprinklers will be provided.
How do we deal with combustible and limited-combustible thermal insulation to ceilings or soffits? If the structure is non-combustible, does combustible insulation trigger a need for sprinklers above the ceilings? I can not put my finger on specifics in NFPA 13 where guidance on thermal insulation is provided. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Peter Howard
8/24/2022 07:05:58 am
I'd say it depends the amount of combustible insulation.
Reply
schulman
8/24/2022 08:05:02 am
why are they using combustible insulation !?
Reply
Jesse
8/24/2022 08:05:14 am
I agree with Peter. The combustibility of the insulation is the driver. If it exceeds the limits of minimally combustible then yes, it needs to be protected.
Reply
Glenn Berger
8/24/2022 08:06:29 am
Encase the combustible insulation inside non-combustible envelope-type assembly.
Reply
Dan Wilder
8/24/2022 08:09:37 am
In 13-19' Edition:
Reply
Todd E Wyatt
8/24/2022 08:15:07 am
The scoping Code, where an automatic sprinkler system (ASPS) is required, is per the adopted Fire Code (e.g. 2021 IBC/IFC). The referenced standards (NFPA 13) by the scoping Code outlines how the ASPS is to be designed, installed, tested, and maintained.
Reply
Alex
8/24/2022 09:52:16 am
Hi,
Reply
Franck
8/24/2022 11:09:16 am
If it is combustible insulation, you need sprinkler protection.
Reply
8/25/2022 02:05:32 am
The problem with combustible insulation is that it can sag before sprinklers activate and affect the water spray pattern, in extreme cases it can even wrap around the sprinkler. As everyone has recommended replace with a certified incombustible product
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |