We have a steel aircraft storage hanger Group 1. It's approximately 50-ft high with exposed steel columns requiring a fire rating per NFPA 409-2022 Edition.
The steel will not be fireproofed but will be protected with sprinklers in accordance with NFPA 409 5.6.3.4. Can pendent sprinklers, installed sideways, be used to satisfy NFPA 409 for column protection? In the past we have protected the columns with sidewall sprinklers spaced according to 409 and on alternating sides of the column. Then the sidewalls were changed to pendent sprinklers installed horizontally to provide better spray distribution on the columns as the sidewall spray tended to (in theory at least) bounce the spray back in stead of vertically. This approach has been accepted by EOR and AHJs alike. NFPA 409 states that "wetting of the lower sprinkler should be considered" although multiple level sprinklers were never used. I'm not sure how this plays in. I recall reading that pendents installed horizontally could be used for column protection due to better spray distribution, however, I cannot find that in code. The client is not open to fireproofing or intumescent paint; column sprinkler protection is in the bit and is going to be used. All is appreciated! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
1/11/2024 07:54:48 am
There are several sections within NFPA that state "Sidewall" specifically, others just reference nozzles or open-head sprinklers along with the GPM requirements based on area of coverage. I'm not seeing a 409- 5.6.3.4? You did not specify if the sprinkler protection was a closed or open sprinkler design. IMO, if closed, stick with a sidewall, if open, allowable in any orientation. If the EOR/AHJ has bought off on the AMM approach, document appropriately and pipe-on!
Reply
Kimberly Olivas
1/11/2024 09:37:52 am
So, would a horizontal sidewall with the deflector to the side be the best, then you get the 180 degree spray going up and down on the column, is that you were envisioning?
Reply
Dan Wilder
1/11/2024 01:22:17 pm
No, but I can see that inference.
Fred Walker
1/11/2024 08:41:08 am
NFPA 409 is open on this, leaving compliance to NFPA 13 with the limited guidance in Chapter 7. Don’t read more into 409 than is there, if the column protection complies with NFPA 13 and the limited requirements of NFPA 409 Chapter 7 then 409 is satisfied.
Reply
Jesse
1/11/2024 09:31:31 am
Agree with everything here thus far. Its easy to read too much into standards.
Reply
O.P.
1/11/2024 11:10:53 am
As I originally posed the question, I was more inclined to go with the pendent in the horizontal position, due to anticipated "bounce back" from a horizontal discharge, However, as Dan stated, " The intent is wetting in a downward direction".
Reply
Patrick Drumm
1/11/2024 01:09:57 pm
O.P. I appreciate your original question because although you observed something in the field that had been previously installed (swapping of sidewall to pendents in horizontal position), you still want the code back-up to perform that type of installation in the future. I sometimes find others simply see things in the field and assume they were done properly and that is a dangerous game to play.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |