There's many code contingencies that depend on a fully-sprinklered building. If a room within a fully-sprinklered building is protected with a clean agent system (per NFPA 2001) and sprinklers are omitted from that room, does the building still meet the criteria to be considered fully protected and qualify for the numerous code contingencies?
Posted anonymously by a member for discussion. Discuss this | Subscribe.
10 Comments
Adam Hicks
11/26/2018 10:23:31 am
F
Reply
11/26/2018 10:33:38 am
The building would not count as Completely sprinkled, therefore would not count for allowances during building area analysis, nor for increases in MAQ.
Reply
Michigan
11/26/2018 10:35:15 am
We are an IFC location, under IFC, a system complaint with NPFA 2001 without a NPFA 13 system in the room does not meet the requirements of fully sprinklered building. This also means that any Building Code "give" for a sprinklered building would not be applicable. I can try to find the code section when I return if that is necessary.
Reply
Michigan
11/26/2018 10:37:25 am
IFC 2015 edition, 903.3.1.1
Reply
sean
11/26/2018 11:07:41 am
904.2.1 Restriction on using automatic sprinkler system
Reply
Pari
11/26/2018 10:51:34 am
IFC ,Section 904.2.1 : Automatic fire - extinguishing system shall not be considered alternative for the purposes of exceptions or reductions allowed for automatic sprinkler system or by other requirements of this code.
Reply
Jennifer Olson
11/26/2018 11:14:30 am
What if it is a small telecom closet that the clean agent system is protecting? Would the telecom equipment be considered "electrical equipment" in which if the room is 2 hour rated and only houses dry electrical equipment, it does not require sprinklers and the clean agent is above and beyond?
Reply
Peter
11/26/2018 11:35:42 am
Jennifer, I think it is a stretch of the imagination to define a telecom room, a data processing room or other a low voltage control room as an electrical room for purposes of exempting it from sprinkler coverage under NFPA 13, even with the 2-hr rating and the other 3 criteria in 8.15 being met. The important thing to consider is the reasons we want the "fully sprinklered" designation is to keep fire flow demand low, to keep standpipe demands low, and to lessen the requirements for detection and others under the IFC. A key point to remember is that an exemption for a small area can be approved by the AHJ. If the AHJ is completely unwavering in his application of the code, then we can add a double-interlock preaction system with dry-pendent sprinklers to the clean agent protected area, and still have a reasonable degree of certainty that the room will stay dry. Yes, it will be at an additional expense to the owner, and yes- it will be beyond our control.
Reply
Jennifer Olson
11/26/2018 04:09:29 pm
Peter, thank you for your reply-it does help a lot. Since I cannot find a location in NFPA that defines "electrical equipment", what are the reasons that telecom equipment wouldn't be considered "electrical equipment" for this purpose? Is it that there would be more cables that would be a different fire hazard than just electrical wiring and machines?
Peter
11/27/2018 08:25:08 am
Jennifer, Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |