High-rise office building, predominantly light hazard occupancy. Water supply is designed for a 30 minute duration (roof mounted gravity water storage tanks).
We need a 1-hour separation between two tenant spaces. The architect has specified a glass partition. As such closely spaced heads are being proposed to achieve an equivalent rating. Does the water supply now need to be upgraded to provide a 1 hour supply of water? Similarly, if sprinklers are being used to provide an equivalency rating on a required 2-hour rated partition, does the water supply need to be able to supply 2-hours of demand? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Salvatore Izzo
12/12/2019 10:18:49 am
Sprinklers used for protection of glazing must be specifically listed to provide an actual fire resistance rating. This website already has some excellent clarifying information on glazing protection:
Reply
Mike
12/12/2019 01:10:21 pm
Must check what the glazing design actually is. Window sprinklers have very specific designs to which they may be applied and therefore have VERY limited applications. The most stringent is mullions.
Reply
Cliff
12/12/2019 01:28:14 pm
The answer is yes, if the sprinkler system, utilizing closely spaced heads, is used in lieu of a 1 hour or 2 hour fire rated partition, the sprinklers need to be able to operate for that period of time.
Reply
Randy
12/12/2019 04:05:48 pm
There's not really enough specific code information here to say definitively. My general take:
Reply