When using loop hangers in fire sprinkler systems, is there a distance (minimum or maximum) that the end of the all-thread rod needs to be from the top of the steel pipe?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
DW
6/9/2022 08:10:49 am
Our state (South Carolina) requires the all thread rod touches the top of the steel pipe. I feel this is a common requirement, I just can't speak for other areas. We are also in a seismic zone, so if we hang the pipe with rod lengths less than 6" we get to eliminate most of the seismic bracing too.
Reply
Dave L.
6/9/2022 10:32:31 am
It should be noted that the 6" length for eliminating lateral bracing is measured from the top of pipe to the point of attachment, so a 6" long rod would pretty much have to touch the top of the pipe.
Reply
Anthony
6/9/2022 08:12:15 am
TLDR: No, mostly.
Reply
David G Kendrick
6/9/2022 08:12:49 am
Depends.
Reply
Alex
6/9/2022 08:15:05 am
Hi,
Reply
James Phifer
6/9/2022 08:15:43 am
Figure A.9.2.3.4.4(b) NFPA 13: 20116 ed shows the rod touching the top of the pipe as a way to prevent upward movement of the pipe.
Reply
JI
6/9/2022 08:16:35 am
A minimum of one thread exposed would make sense. Many stud specifications I have seen call for a minimum of one to three threads exposed. As long as the threads are fully engaged into the swivel nut I would consider it acceptable.
Reply
Ryan Hinson
6/9/2022 08:51:02 am
Agree with the other posts above. Keep in mind that, if pushing piping through a hanger that is already installed, the tip of the ATR (likely cut quickly deburred with a chop-saw) may have a sharp tip in contact with the the pipe which can potentially scratch the pipe longitudinally. While not a big deal on black steel; this can be a big no-no on other types of pipe where external coatings need to remain intact for longevity of corrosion-resistance or for listed-installation requirements such as for CPVC where scratches are detrimental to the pipe's integrity.
Reply
Julie
6/15/2022 10:40:33 am
AHJ inspector here, when working at a major city in California, we required the thread to be in contact with the pipe. Here in Nevada, I have never seen another inspector enforce this or even mention it. I never see the threads touching the pipe here. I have tended to do what the others in my area are enforcing so we are consistent. I suppose that just means it depends on your AHJ if it’s not in code.
Reply
Chris
6/15/2022 05:34:03 pm
AHJ here for a fire dept (part time job) also licensed in the state of Ohio (full time job) for sprinklers, eletric fire pumps, diesel fire pumps, fire alarms, portable extinguishers, pre-engineered systems.
Reply
Chris
6/22/2022 12:47:39 pm
AHJ here for a fire dept (part time job) also licensed in the state of Ohio (full time job) for sprinklers, eletric fire pumps, diesel fire pumps, fire alarms, portable extinguishers, pre-engineered systems.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |