Assuming that it's been approved by a structural engineer, is there any code or standard restrictions that would prevent running CPVC branch pipe through a built-up floor beam?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
7/21/2022 06:17:38 am
Hi,
Reply
Anthony
7/21/2022 08:08:23 am
What Alex said.
Reply
Jesse
7/21/2022 08:08:56 am
Certainly, as long as the structural engineer approves of the approach.
Reply
schulman
7/21/2022 08:30:46 am
common sense usually dictates cutting holes in beams is a last resort. can't imagine a situation where this is the last resort.
Reply
Michael J Riola
7/22/2022 08:14:24 am
Recently had a job where 14' ceilings weren't enough. We coordinated penetrations in brand new steel beams!!
Reply
Casey Milhorn
7/21/2022 09:11:40 am
Also, if this is a seismic job, don't forget about additional clearance that may be required, which could make for an even larger hole through the beam. Most beams we've penetrated go by the third rule. Penetration has to be no more than 1/3 of the depth of the beam, located in the middle 1/3 of the beam vertically, and located within the middle 1/3 of the span. As you stated though, only with very clear instructions, in writing from the structural engineer (preferably the EOR and not one that you or the GC hired). If this is a retrofit situation and there is not a structural EOR, the structural engineer should be hired as far up the chain as possible. If the GC is smart, they will have the owner hire the structural engineer, or at least the architect.
Reply
Joe Chadwick
7/21/2022 09:58:37 am
Running CPVC through anything: I’d get a letter of compatibility for any adhesive or FR treatment in the beams. It doesn’t have to be in intimate contact to cause trouble.
Reply
Julius Wanyandeh
7/25/2022 08:18:47 am
It is allowed but must be way-off the centre of the built up floor beam.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |