Is CPVC allowed to be run exposed through a small storage room?
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Alex
1/1/2024 10:11:13 am
There is nothing that says it is not permitted, contingent it meets the manufacture guidelines. I would defer to the cut sheet of the piping you are using on your project.
Reply
Mark Harris
1/1/2024 12:43:34 pm
Agree with Alex to look at the listing. Was long time ago but I remember some projects where we transitioned to steel for the exposed pipe in kitchen and storage rooms.
Reply
Ricardo Sellek
1/2/2024 03:37:41 pm
The CPVC cannot be exposed in kitchens due to the presence of grease laden kitchen exhaust which if I remember correctly can possibly breakdown the pipe over time.
Reply
Glenn Berger
1/1/2024 06:32:03 pm
It depends on the actual size and contents of the storage room. The term small is relative; likewise with the term of room names being storage.
Reply
Jesse
1/2/2024 07:35:10 am
Agree with Glenn here. "Small" doesn't tell us much. CPVC is listed for Light Hazard, and this storage room likely won't be Light Hazard. CPVC can be used for small areas of OH1 / OH2 occupancies, generally less than 400-sq, ft.
Reply
DE
1/2/2024 09:02:04 am
My response is based on the CPVC product that we use.
Reply
Randy Kimbro
1/2/2024 10:36:53 am
As an AHJ, we have been through this in detail over the last few months on two construction projects. If you are using BlazeMaster CPVC, it must be protected behind drywall or drop ceiling. Or if run exposed it can only be installed against a flat horizontal ceiling. The BlazeMaster installation manual is very specific about this and we confirmed all of those details directly with BlazeMaster. I hope this helps.
Reply
sean
1/2/2024 08:59:16 pm
many cpvc manufacturers now allow accessory room 400 sq.ft. or less to have sprinkler piping to be cpvc
Reply
Danial Bartle
1/3/2024 07:49:54 am
The temperature rating of the heads cannot be above 165 either.
Reply
Mike
1/19/2024 02:38:36 pm
Check the manufacturer listing. Storage is not light hazard.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |