What are the physical or regulatory concerns of leaving an older dry pipe valve as wet for an extended amount of time?
This would be during the non-freezing months. I can think of the alarm trim - water gong changed to electric, clapper gasket integrity, and the inevitable leaks in the overhead system. Curious on other perspectives, thank you!
9 Comments
Pete H
4/11/2023 06:43:51 am
The immediate problem I can think is this will void the listing of the assembly.
Reply
Anthony
4/11/2023 07:19:07 am
Well, your system will be under "impairment" because the alarms wort work. the pressure switch on the valve will be constantly going off and that's your means of alerting your alarm system to sprinkler flow. (as Pete mentioned above).
Reply
Alex
4/11/2023 07:23:32 am
As others mentioned, you won’t have a means for alarm.
Reply
Casey Milhorn
4/11/2023 08:07:18 am
I've done it several times (at owners request in writing) and of course need to remove the pressure switch(es) and add a flow switch. I would also highly advise Nitrogen and purge valve, even if its just one of the cheap bottle set ups.
Reply
SCHULMAN
4/11/2023 08:14:42 am
Could someone explain WHY you would do this?
Reply
Casey Milhorn
4/11/2023 08:32:06 am
Air compressor goes out and/or they are tired of dealing with the maintenance of a dry system (and of course they intend to keep the space heated at a min of 40 degrees). Not my favorite thing to do, and we of course advise they let us install at least a shotgun type wet riser, but it's almost always about the $$$.
Reply
Jesse
4/25/2023 10:01:59 am
Wondering the same
Reply
Franck
4/11/2023 10:02:06 am
Believe it (or not) but this dual systems were quite common in France about 20 years ago. We called them "Alternative sprinkler systems" as they were alternatively wet or dry.
Reply
Anthony
4/11/2023 12:27:12 pm
"If the system is well designed to fight a fire in the winter time, then it is fine to control the same fire under the same conditions during the summer time." <- this
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |