2015 NFPA 101: A college classroom building is a Business occupancy. For occupant load relative to the classrooms, do you use the Educational amount of 20 SF net or do you use the Business square-footage amount? In the past, we’ve used the Education load because it seemed logical; but is this correct?
Posted anonymously by a member for discussion. Discuss this here.
15 Comments
Roy
10/18/2018 09:18:03 am
In my opinion the 20 SF is correct for Classroom areas.
Reply
Edw H
10/18/2018 09:34:20 am
K-12 are Educational
Reply
Roy
10/18/2018 09:52:03 am
EDW what is the sqft per person in NFPA 101 for a classroom?
Reply
Jon Nisja
10/18/2018 09:55:16 am
Occupancy classifications and means of egress occupant load factors are two different things. While the terminology is similar, they are not interchangeable concepts. For egress purposes, a classroom use is classroom use - it doesn't matter if it is in an elementary school, high school, college classroom, or adult education.
Reply
MAX
10/18/2018 10:11:41 am
College and Universities are considered a business occupancy. But, occupant load is calculated on use of space and not the occupancy classification. I agree with 20 sq ft.
Reply
Pari
10/18/2018 10:22:28 am
I agree with Jon Nisja , The set up of the room is classroom therefor means of egress shall follow the same rule of educational facility but laboratory and vocational shop is 50.
Reply
Ginger
10/18/2018 11:59:47 am
As an FPE consultant I calculate the occupant load and exit capacity of buildings on a daily basis. We work on a lot of college campus building and we get this question frequently, since the architects want to use 100 sf/p instead of 20 sf/p for classrooms because it results in more desirable occupant loads. Ultimately, it comes down to the use/function of the space. Per Table 7.3.1.2 of NFPA 101 the occupant load factors are based on uses and not occupancy group classifications. Therefore, you can have a Group B, higher education/college building that has classrooms that have occupant loads calculated at 20 sf/p. Faculty or Grad Student offices would be calculated based on the office function of 100 sf/p. Conference rooms, lounges, cafes, etc. with assembly functions would be calculated at 15 net sf/p for non-concentrated assembly functions.
Reply
RON PIERCE
11/5/2019 02:26:16 pm
Thanks for the clarification! Never would have thought that Occupancy Classification would be different than Occupancy Load, but I can see it now after rereading NFPA 101. Would be nice if they could better at delineating the subjects. So I was asked again today, "How many can we fit in this classroom?", and I can rely on 20 sf/p as a general standard...correct (given not assembly or other unique usage)? Thank you all for your input.
Reply
HPeterson
2/11/2019 01:43:09 am
So you calculate the occupant load for classrooms, etc. OLF for classrooms is net. How do we calculate for additional students occupying corridors outside classrooms while classes are in session?
Reply
MODERATOR
2/22/2019 07:02:10 am
HPETERSON, Good question - this is being discussed currently as a Daily Discussion topic.
Reply
Couple O'Pennies
10/5/2022 09:03:52 am
In this case the definition of "occupiable space" may come to bear. Corridors and toilet rooms are not "occupied"; it helps to think of them as "transitory" spaces. Spaces like mechanical or storage rooms can be occupied by people working in those spaces, but the load factors are larger to account for the lower density of people. You don't find corridors, toilet rooms, foyers, etc in the occupant load tables, likely because they are not considered "occupied" spaces.
Reply
Ron Pierce
3/7/2019 03:54:50 pm
We're having this sort of conundrum at our university-- defining "room capacity". While maximum occupancy is a life safety calculation, OPTIMAL capacity to maximum learning is a whole different topic altogether. Some classrooms look like cattle cars heading to slaughter with so many desks and little aisle space. Is there a simple way I can walk into a room, measure it, and come up with a maximum room capacity? Is this something I can use the load factor table to accomplish? It still seems there's disagreement between using the Education LF (20SF) versus the Office LF (100SF) for college classrooms. OLF would make our classrooms look barren!
Reply
John smith
7/22/2019 01:08:08 pm
The 2012 commentary states the following
Reply
John Smith you are correct. The 2018 NC Fire and Building Codes state that for a Business use, which is education above the 12th grade, you can't classify the Assembly spaces as classrooms. The egress is calculated at 15 sf/p and the occupant load is calculated on the Business use. The NFPA table in chapter 14 explains this very clearly. The confusion comes in with the wording of "classroom". You can only find that wording under Educational use. Not under Business use
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |