We have storage of Class I-IV commodity, in racks, with maximum distance from floor to top of storage of 12-ft with 10-ft aisles and roof deck at 25-ft.
The AHJ correctly asserts that this storage is not incidental to the occupancy and therefore cannot be considered as "miscellaneous storage". Is there a way that these racks can be suppressed with roof-only sprinklers, preferably CMDA or CMSA? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
9/29/2023 07:14:07 am
Yes, you can get away with ceiling only protection using CMDA - NFPA 13 (2013) Table 16.2.1.3.2
Reply
Pete H
9/29/2023 07:28:21 am
It's not miscellaneous storage.
Reply
Glenn Berger
9/29/2023 08:08:23 am
I concur with the opinion that opinion that you do not have miscellaneous storage.
Reply
Casey Milhorn
9/29/2023 09:58:40 am
I agree with everyone. You probably have low piled storage and will follow those guidelines. You will have to go through the different options to compare CMDA, CMSA, ESFR, etc. Keep any group A plastics below 5', Class IV below 10', and you will be at a very reasonable demand.
Reply
Randy rathert
9/29/2023 10:24:51 am
Im still learning here, so can you explain what OH2,EH2,and EH1 are?
Reply
Joe Meyer
9/29/2023 10:44:08 am
Hi Randy -
Reply
Jesse
9/29/2023 12:35:03 pm
Absolutely you can protect with CMDA ceiling only. Just pick a point on the design curve for protection of C-IV without IRAS
Reply
I agree with the points made earlier.
Reply
Quentin M Maver
10/4/2023 10:52:07 am
HIGH-PILED COMBUSTIBLE STORAGE. Storage of
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |