My question is when the discussion of dirty sprinkler heads comes up I get told only lint , hair and fuss count.
What I see quite often is discoloring from what I assume oil running down the pipe to the head. I also often see the red glass turned to black or gray. Do these sprinklers need to be cleaned, and if so, how is it done? Air or vacuumed doesn’t always work. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Dan Wilder
1/14/2021 08:31:14 am
NFPA 25 Annex has some language about these specific questions.
Reply
Alex Jenness
1/14/2021 09:16:54 am
As an AHJ inspector I would require replacement of a head with a discolored bulb, unless it's been exposed to sunlight or cold and considered okay (NFPA 25 A.5.2.1.1.1). For loading, if a manufacturer has an approved cleaning method, I'm okay with that. Oils on the bulb are concerning as they may absorb heat differently, or insulate the bulb and cause pre-mature or failure to activate.
Reply
Jim Auer
1/14/2021 09:39:58 am
Agreed with comments above from Dan. The only option given to clean is compressed air or vacuum. My interpretation/understanding is that once the sprinkler is installed... Don't touch it.
Reply
Ryan Grant
1/14/2021 04:08:41 pm
I would always consult the AHJ. But as an inspector, if that head has oil on it it would be deemed needing replaced. Like Alex, if the bulb is discoIored, I would also order that head replaced.
Reply
Felipe Pedraza
1/14/2021 04:17:52 pm
This is a good concern. NFPA 25 does provide language regarding the cleaning of sprinkler heads and how it should be done.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |