We have a wet pipe system in a conditioned space.
If this is converted to a dry pipe system for the purpose of installing a nitrogen generator - would the existing pipe need to be sloped? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Ryan O'Hara
8/11/2022 08:05:15 am
Installing a N2 generator on an improperly sloped system will not have the same benefits of a system that drains correctly.
Reply
DW
8/11/2022 08:09:35 am
My understanding of retrofitting systems with Nitrogen, is that a lot of the corrosion inhibiting is based on a properly installed dry system. A local nitrogen generator rep states that pipe having the correct slope is important for the nitrogen to do it's job properly. Plus, sloped mains and branch lines are requirements of dry systems in NFPA 13. I would say yes the pipe needs to be sloped, and maybe additional test and drains added as well. You should check out the nitrogen options for wet pipe systems. South Tek has an option available that I know of. It may be less hassle to leave the wet system in place and utilize a wet system nitrogen system.
Reply
Dan Wilder
8/11/2022 08:12:31 am
There is no distinction for Dry or Preaction piping systems for slope/pitch requirements for conditioned spaces, only for refrigerated spaces, the piping would need to be pitched per 13-19 16.10.3
Reply
Rob B
8/11/2022 08:29:26 am
Unless I am reading this wrong, In general Dry piping needs to be pitched when installed?
Reply
David G Kendrick
8/11/2022 08:16:46 am
Agree with the sloping and additional drains.
Reply
Alex
8/11/2022 09:00:17 am
Hi,
Reply
Jesse
8/11/2022 09:25:02 am
Yep, you'll need to slope the branch lines and mains per NFPA 13. You'll probably need low point aux. drains as well.
Reply
Anthony
8/11/2022 09:52:28 am
Yes, all dry pipe need to be pitched per NFPA 13-19 and NFPA 13-16.
Reply
Kody Karch
8/12/2022 09:47:21 am
Unless there are other circumstances I am not aware of, wet pipe inerting would be your best course of action.
Reply
8/12/2022 03:52:48 pm
Needs to be sloped per 16.10.3.1 - Dry Pipe Systems in Nonrefrigerated Areas. In dry pipe system, branch lines shall be pitched at least 1∕2 in. per 10 ft (4 mm/m), and mains shall be pitched at least 1∕4 in. per 10 ft (2 mm/m) in nonrefrigerated areas.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |