I am doing an evaluation of a water supply for a fire sprinkler system. The system is an ordinary hazard wet pipe fire sprinkler system. It was designed as a pipe schedule system. Table 19.3.2.1 of NFPA 13 – 2019 Edition gives the water supply requirements for Pipe Schedule sprinkler systems.
Based on our buildings construction the table requires that for Ordinary Hazard we have a 1,500 gpm flow with a residual pressure of 20 psi. Section 19.3.2.6.1 then states, “The residual pressure requirement of Table 19.3.2.1 shall be met at the elevation of the highest sprinkler.” My understanding of this requirement is that if I have a pipe schedule system where the highest sprinkler head is 20 feet above the finished floor which equates to roughly 8.7 psi of head I would need to have a water supply that provides a minimum of 28.7 psig residual water pressure flowing 1,500 gpm to the base of the riser to meet the requirement. Am I calculating the required residual pressure correctly? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Casey Milhorn
6/3/2021 08:14:44 am
That is my understanding of the requirement.
Reply
Mike F
6/3/2021 08:17:25 am
In addition to your SHP which is 20 psi and your elevation which you calculated to be 8.7 psi. If your system has been retrofitted with a BFP assembly you need to also add that to the calculation. When all is said and done, you should have at least 20psi at your most remote head.
Reply
Jay
6/4/2021 03:29:44 pm
20 psi is not required at the remote head.
Reply
Dan Wilder
6/3/2021 08:35:45 am
The approach looks correct, just don't forget about any backflow loss that would need to be added in (at the 1500GPM flow loss point).
Reply
James Phifer
6/3/2021 10:19:25 am
You forgot to include the starting pressure of at least 7psi.
Reply
Jay
6/4/2021 03:31:45 pm
Pipe schedule systems are not based on calculating 7psi at the remote head.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |