I am an AHJ and have a salt spa in our jurisdiction with sprinklers in the salt therapy room. Not surprisingly these sprinklers are heavily coated with salt deposits.
What is the best type of head to use in this environment? If we require wax-coated corrosion resistant heads we are still concerned with salt deposit build up. Any other suggestions on ways to protect heads in this room? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Craig S
7/12/2021 07:40:45 am
I would say that if the concern is corrosion, your best bet would be either a wax coated or a polyester coated heat (like a white semi-recessed sprinkler). These are both safe choices for corrosion resistance. If your concern is for buildup, your best bet might be to go with a concealed head with a cleanroom gasket. This will protect the sprinkler element from any salt, and the cover plates can be more easily wiped down by staff as needed.
Reply
MattC
7/12/2021 08:38:30 am
I agree with Craig above.
Reply
Justin Phillip Milne
7/12/2021 09:43:07 am
I agree with Craig and MattC on the corrosion topic. Only adder is that some sources state a salt fog environment 20% or greater needs to be UL 199: Standard for Automatic Sprinklers for Fire-Protection Service listed. At least that's my understanding.
Reply
Brad K
7/12/2021 10:02:48 am
I was thinking the same as the above from Justin.
Reply
CJ Bonczyk
7/12/2021 09:44:57 am
We have used in many areas where the atmosphere was corrosive the Victaulic Firelock PTFE, VS-250, or Stainless Steel sprinklers. The sprinklers themselves have a UL & FM listing for various types of corrosion resistance. If you contact there technical assistance department and give them the compounds and or chemical percents that the sprinklers will be exposed in the atmosphere the most they will tell you which coating is best for your application.
Reply
Jay
7/12/2021 09:58:40 am
I would use standard heads but protect them using the rules in NFPA 13 for paint spray areas, by covering the heads with cellophane or thin paper bags. See 2016 NFPA 13:22.4
Reply
Pete
7/12/2021 10:27:57 am
My "hot take" poorly researched answer that doesn't know the level of salt build up already observed in these spas:
Reply
franck
7/12/2021 11:39:51 am
Believe it or not, but salt spa should have more salt built up on sprinklers than altt storage rooms.
Reply
Randy K.
7/12/2021 11:08:15 am
All excellent comments and suggestions! These help us quite a bit. Thank you each for your insights and expertise.
Reply
Franck
7/12/2021 11:36:17 am
I would go for corrosion resistance sprinklers (as mentioned above), combined with a cellophane or thin paper bag.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |