In your opinion, what's the best way to address sprinkler design when there are open breezeways separating units in the same building?
Do you somehow provide a heated chase under a deck? Convert from CPVC to steel and heat-trace a run? Go back underground and potentially "under" the building? Use separate risers for each grouping, bumping up the price significantly? Residential multi-unit apartment complexes are frequently built with open breezeways in-between blocks of units. These usually have paved concrete at the bottom, only wood joists and decking for stairways and walking areas, and a covered roof at the top. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Jonathan Sullivan
3/30/2020 10:10:58 am
Depending on the site layout, individual risers/building are the best from an operations perspective. If that is too complicated, heat trace is a good approach; I prefer not dealing with underground unless unavoidable. I do not know what your secondary power availability or climate are, but I think it's a good idea to have this system on standby or emergency power.
Reply
Thomas Reinhardt
3/30/2020 10:16:51 am
Is breezeway even a definable term in the building code. Maybe you mean walkway?
Reply
Darren Englert
3/30/2020 11:00:17 am
I have used several methods to feed the other side of the open walkway. The method you use is very dependant on the climate where the building is being built. I live in an area of the country where we do not get sustained freezing temperatures, so some of these suggestions may not be advisable in your area.
Reply
Anon
3/30/2020 12:08:30 pm
Depends on what part of the country. In the south we cross the breezeways with sleeves, protect the breezeways with dry sidewalls, and run wet pipe in the attic with plastic tenting between the insulation and piping. You can also "bird cage" it using sidewalls to keep the wet piping out of the attic.