Hello all, two questions:
1) Can the rules of a beam obstruction also be used for a 4 ft (1.2 m) obstruction? Or does section 8.5.5.3.1 prohibit that arrangement? 8.5.5.3.1* Sprinklers shall be installed under fixed obstructions over 4 ft (1.2 m) in width. 2) Can the rules of a beam obstruction also be used for a 30 in (750 mm) against wall obstruction? The standard says sprinklers "8.6.5.1.2*... shall be arranged to comply with one of the following arrangements" Or does an obstruction against a wall have to comply with Figure 8.6.5.1.2(b) and then has to have a sprinkler underneath? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Mike
5/14/2020 10:09:08 am
Not sure I understand what you mean.
Reply
Jonathan Joseph
5/14/2020 10:34:36 am
8.6.5.1.2 Standard Spray Table. 2016ed
Reply
Anon
5/14/2020 11:36:51 am
Forgive me if I am interpreting your question incorrectly, but is this like a soffit against a wall?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |