We are designing a foam system (not a water spray) protecting an industrial facility.
Two systems are being designed, and they're located side-by-side. The two systems are not currently interconnected, but I believe they should be and balanced. We're getting some pushback on our approach and I'm interested in other opinions here. Do the system volumes need to be combined and compared to the available water supply, or can each system be calculated separately (but still flowing at the same time without balancing)? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jay
10/19/2022 08:29:39 am
Are the 2 systems required to be designed to flow at the same time?
Reply
Alex
10/19/2022 08:31:17 am
Hi,
Reply
Connor
10/19/2022 08:42:58 am
If the systems are not required to flow at the same time, they can be calculated separately.
Reply
Dan Wilder
10/19/2022 08:43:45 am
Is the expectation that both systems will discharge together? If yes, then the calculation would be accurate for both discharging (balancing, total foam required, available water supply comparison...) however why not make them 1 system not just interconnected (unless the volume requires two valves, but you'll have to get some version of an inline flow control proportioner to help the foam ratio's)?
Reply
Brad K
10/19/2022 08:46:30 am
We may be short on information here but it feels like two non-interconnected foam systems exist. It may be a scenario where a draft curtain or partition should be proposed if they are not to be interconnected and balanced. Independent systems need independent balanced foam proportioning and available water supply. Are we talking about two systems with single foam concentrate storage? Keep in mind proportioner flow minimums if there is any chance of a partial system discharge adjacent to another.
Reply
Todd E Wyatt
10/19/2022 08:47:54 am
Below are the NFPA standards related to foam systems :
Reply
Joe Brill
10/19/2022 09:00:55 am
Water supplies shall have the capacity and a pressure to maintain foam and/or water discharge, or both at the required design rate for the required duration over the area protected by the systems that are expected to operate simultaneously. NFPA 11, 4.2.2.2.2
Reply
Jesse
10/19/2022 10:20:46 am
Its hard to tell from the OP, but it sounds as if the systems are intended to flow at the same time. Is there something that would prevent them flowing at the same time? How are they actuated? Separate fire areas?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |