NFPA 20 5.6.2 requires a fully-independent and automatic back up pump for very tall buildings. This project is just under 50 stories with a pump and back up several levels below grade serving the lower zones and another pump and back up several levels above grade serving the remaining zones.
The project’s electrician cannot meet the power requirements for the worst case scenario, which would be all (4) pumps operating at once (if the primaries are running, but not at full capacity). The request is to interlock the primary and back up on the respective level, so only one pump is running on the level at a time (for a max total of two pumps running in the whole building). Would interlocking the pumps on their respective levels still satisfy the requirements of NFPA 20 5.6.2 (copied below)? NFPA 20 5.6.2 Fire Pump Backup. Fire pumps serving zones that are partially or wholly beyond the pumping capability of the fire department apparatus shall be provided with one of the following:
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Todd E Wyatt
5/12/2021 08:59:05 am
I would recommend starting in the scoping Code (e.g. 2021 IBC) for the fire protection requirements for a "high-rise building" (HRB).
Reply
Jay
5/12/2021 04:25:55 pm
913.1 requires the fire pump to be installed in accordance NFPA 20. That means the entire standard and not only certain sections of NFPA 20, except where there are conflicts between NFPA 20 and the IBC/IFC, in which case the IBC/IFC governs.
Reply
James
5/12/2021 04:31:01 pm
Agreed; once a fire pump has been introduced I've always understood the whole standard of NFPA 20 to be applicable.
Todd E Wyatt
5/13/2021 08:40:25 am
Per the scoping Code (IBC), it states :
Reply
Jay
5/13/2021 02:15:41 pm
913.1 prescribes the use of the entire referenced standard, NFPA 20, not only specific sections of NFPA 20.
Domingo Chinel
9/1/2022 09:34:00 pm
thank you for the knowledgeable information you share .
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |