NFPA 20 Section 4.15.5.1 (2016 Edition) requires a listed OS&Y gate valve to be installed in the suction pipe, but the annex of NFPA 20 suggests it should be as far as practical from the pump suction.
Would a control valve (OS&Y) on the backflow preventer meet this control valve requirement of Section 4.15.5.1? Assuming a city water supply, the backflow preventer control valve is listed for fire protection, there is still a valve'd bypass connected between the backflow preventer and pump suction, and the backflow is located a minimum of 10-pipe diameters from the suction flange. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
5/24/2021 08:39:39 am
The location of the bypass needs to be upstream of the suction gate valve. This will allow the use of the bypass while servicing the pump.
Reply
CJ Bonczyk
5/24/2021 09:48:11 am
OSY is still required to isolate pump for service, and allow city supply be connected upstream. This way, city supply still runs through BFP when the bypass is in use.
Reply
Casey Milhorn
5/24/2021 11:06:57 am
What Glenn and CJ said. But if you don't have a bypass I guess the backflow OS&Y could serve as that valve. On the other hand, if you don't have a bypass that probably means you have a tank only supply and don't need a backflow. Pretty rare to have a backflow without need for a bypass as well.
Reply
Franck
5/25/2021 03:47:30 am
As often, the answer will be "it depends"
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |