Can an assisted living facility that installed a an NFPA 13 compliant system which was only required to be a 13R now remove the dry attic part of the system?
They have had corrosion issues and leaks they are wanting to avoid. The only reason they installed the 13 system is initially they envisioned possible adding a skilled care section which is now not happening. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Dan Wilder
1/9/2024 07:11:14 am
You'll run into several issues and questions:
Reply
Anthony
1/9/2024 07:48:48 am
Yes you can remove the system if the attic protection was above and beyond code requirement. Make sure you have all your ducks in a row as Dan mentioned, this may not be as cut and dry(puns intended) as you think.
Reply
Chad
1/9/2024 11:17:42 am
Not if NFPA 1 applies. Non-required systems stay unless permitted by the AHJ.
Reply
Glenn Berger
1/9/2024 08:15:33 am
Proceed with caution on this subject. Need to do a full code analysis on the exact conditions of this specific facility. I have been to several assisted living facilities and they are more than your basic apartment style buildings.
Reply
James
1/9/2024 08:27:10 am
I agree with emphasis on needing the "full code analysis" part.
Reply
Nelson
1/9/2024 08:59:09 am
I agree that a "full code analysis" will be needed.
Nelson
1/9/2024 09:05:15 am
Correction........13R is for life safety only. Sorry for the typo.
Todd E Wyatt
1/9/2024 08:54:48 am
Q : Can an assisted living facility that installed a an NFPA 13 compliant system which was only required to be a 13R now remove the dry attic part of the system?
Reply
Todd E Wyatt
1/9/2024 08:55:40 am
REFERENCES continued ...
Reply
Pete H
1/9/2024 09:48:04 am
Agreeing with everyone else, it theoretically can, but if the architect used anything that required the building to be NFPA 13 or fully sprinklered for ICC code compliance, you've now opened that can of worms by changing the system.
Reply
Jesse
1/9/2024 10:21:27 am
I would recommend doing a full analysis of applicable code. There's a reason the original install was full 13 and not 13R.
Reply
Todd E Wyatt
1/10/2024 08:43:23 am
"The only reason they installed the 13 system is initially they envisioned possible adding a skilled care section which is now not happening."
Reply
Sean
1/10/2024 07:26:56 pm
Removal of systems is difficult, time consuming, and does not always work out.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |