I had a client ask about Oxygen-Reduced Systems (ORS), aka Hypoxic air technology (displacing ambient oxygen in an enclosed environment such as in warehouses). I did a quick read with what's available on Wiki, FM and NFPA. But even my go-to suppression people have hardly encountered these. Testing has been very specific.
Just to increase my knowledge, does anyone here have an practical experience in these? Are these systems really being installed? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Sean
1/23/2024 08:08:39 am
I would recommend drawing in a vendor like Wagner (there may be others). They have started creating a presence here in the US and we are aware of several projects that have deployed ORS systems in warehouses.
Reply
Glenn Berger
1/23/2024 08:12:03 am
My experience has been vendors telling me that these systems are being installed all over the place without proof.
Reply
Eddie
1/23/2024 08:26:15 am
How does one escape from the center of a warehouse if this system is activated?
Reply
Franck
1/23/2024 11:28:37 am
Eddie
Franck
1/23/2024 11:30:58 am
Fully agree.
Reply
Greg
1/23/2024 08:50:56 am
I did review the oxygen reduced environment as a consideration within an AutoStore system. I'll put a link below as to what an AutoStore system is. My thought as to where an oxygen reduced environment could be considered was in a location that is not normally habitable. No one would normally be inside of the robotic type of storage systems. However, there a numerous safety tradeoffs that must be considered with a hypoxic technology system.
Reply
Jesse
1/23/2024 09:05:02 am
Like Glenn, I've been told they're being installed "all over the place", but have yet to actually see any evidence of it.
Reply
Franck
1/23/2024 11:15:32 am
I yhave seen one of these systems in Sweden, in an electrical room (switchgear).
Reply
Greg
1/24/2024 07:39:54 am
Franck provides very practical and first hand experience about concerns with oxygen deficiency and elevation (higher altitudes). The NIH article cited above in Greg's comment speaks to that in some depth and provides for a calculation - styled consideration. While the article was written from the perspective of wearing respirators, the physiological response to oxygen deprivation is the key - takeaway.
Reply
Franck
1/23/2024 11:24:39 am
Now I will speak about the technical issues.
Reply
Mark Harris
1/23/2024 01:17:22 pm
My understanding Wagner did a system in an automated warehouse in the Northwest a couple years ago. Probably have done more in the states since that. As I recall intent is forr automated storage not for normally occupied. Support areas (docks, offices, etc. would need different protection - sprinklers). The suppression design of taking oxygen below 15 percent would be similar to suppression with clean agent inert gas system. For inert clean agent systems NFPA 2001 states exposure should be limited to 5 minutes for up to 43% design - 12% oxygen and 3 minutes for up to 52% design - 10% oxygen.
Reply
Anonymous
1/23/2024 06:12:58 pm
As the person who posted the question, I thank you all for your insightful and informative comments!
Reply
Pete
1/24/2024 06:14:16 am
My feeling is that there are a lot of technologies that will put the fire out. As an engineer/design pro, we kind of need to do our best to "do no harm " to people, except our mandate takes the form, "hold paramount the safety and welfare..." My mind jumps to the case studies of mishaps, and I try to consider them in the context that nobody set out to intentionally, say, level a school and kill 100 kids. When I have the need to think outside the box to protect some commodity, only as a last resort do I consider CO2 flooding, Halon 1301, high expansion foam, or any other method that could potentially kill someone in the process of protecting the property. Can it be safe? Sure. But, I would only consider after exhausting every other option, and not without a detailed risk analysis and system reliabilty calculation. I'd also consider ongoing maintenance cost and depreciation before choosing a hypoxic system.
Reply
James Art, FPE
1/24/2024 01:16:18 pm
The reduced O2 can be all the time.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |