We have a specification for a project that required calibrated smoke testing for a project that only has two new smoke detectors.
Is there a code basis for this test, rather than just a can of smoke? This project is under UFC 3-600-01 / UFGS spec 283176. The smoke detectors are new from the factory, clean, and I find this to be a relatively useless and expensive test. Would welcome any input/insight here. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
MATT C
11/25/2021 09:40:23 am
Sounds like you're referring to sensitivity testing? Any fire alarm company who conducts annual FA inspections should be able to easily do that for you, as I believe this is an annual testing requirement in most jurisdictions - but this could vary depending on where the project is located.
Reply
Jay
11/25/2021 06:36:50 pm
NFPA 72 chapter 14 requires smoke detectors to be sensitivity tested within 1 yr after installation and then every 2-5 years after. There is no requirement to test sensitivity during acceptance testing.
Reply
Dominic S
12/1/2021 07:13:00 pm
The UFC requirements are typically enforced by the ACOE or Project QC Officer or Installation FPE.
Reply
sean
12/31/2021 06:46:14 pm
the manufacturer tells the process of calibration testing
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |