Sprigs that are over 4-feet in length are required to be restrained under NFPA 13.
What options do we have to achieve this? I'd like to hear some different methods used to do this to expand my own knowledge here. Different situations like construction type and if the structural members are above or below the sprig. Thanks so much. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
4/6/2022 07:14:37 am
Hi,
Reply
Pete H
4/6/2022 07:18:23 am
Taking a shot in the dark, so take with a grain of salt:
Reply
Justin
4/6/2022 08:26:36 am
What we use out in field and have found to have the most and quickest for field installation no matter what building type might be, is rod with swivels and a 1" hanger. The swivel allows you to be at multiple angles. It's what we our guys use on all of our installs that need this. This way and cable allow you the flexibility as a designer so you don't have to hit building members perfectly for clamps. It gives the field guys flexibility as well if other trades may be close or in the way. Installers are already used to using swivels and rod. We also span unistrut between members and attach swivels and rod for the random times the building members are too low or something like that.
Reply
Brad K
4/6/2022 08:31:05 am
Several things we see for this solution. We have used tees in the sprig to arm over and support the sprig below adjacent structure. Unistrut and u-bolt if sprig exists between structure. Lateral sway bracing or 4-way bracing.
Reply
Manny Rios
4/6/2022 09:06:02 am
In our jurisdiction most if not all projects are a seismic zone that requires additional restraint. Taking into account the construction design wires, cables and or rods with swivel clamps have been the preferred products to use.
Reply
Dan Wilder
4/6/2022 11:44:54 am
Any time we've dealt with this:
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |