When a building is 84-feet from an existing public fire hydrant located across a 2-lane 45mph roadway, can we assume it is standard practice to use it in an event of a fire? Or would the owner be required to add a personal-use fire hydrant or water storage device on their side of the road? In the latter case, how far would the fire hydrant have to be placed from the building? Thanks in advance.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Glenn Berger
3/9/2023 08:06:47 am
Unless the AHJ says anything to the contrary, I see no reason why the hydrant across the street cannot be used in case of a fire emergency.
Reply
Scott McBride
3/9/2023 08:17:46 am
The code and standards require that the hydrant has to be no more than 100' from the location of the FDC not the building. Unless the AHJ has added an amendment to change that distance.
Reply
sean
5/8/2023 08:40:57 pm
only for standpipe systems does 100 ft apply
Dale
3/9/2023 08:26:01 am
NFPA 24 is your resource for Fire Hydrants. In the 2016 edition (which is what is in use in my area), hyrdrants are supposed to be located within 40 feet from a building (7.2.3). If they can't be located within 40 feet, then hydrants are permitted to be used where approved the AHJ. I had a project many years ago, where the nearest hydrant was more than 40 feet away. The Fire Chief made the client add a Hydrant to the project (we were doing some renovation in an existing space, along with a new addition to the existing building). "Too much hose" is what he told me. Hope they are OK with the one you got.
Reply
JH
3/9/2023 08:47:18 am
40 ft. is the minimum distance, not the maximum distance per NFPA 24:7.2.3. The "intent" of the code is for the clearance to be at least greater than the height of the building facing wall, known as the "collapse zone". (I believe the IFC establishes this distance as 1.5 times the building height.)
Reply
JH
3/9/2023 08:36:24 am
I tried posting this from my email, so I apologize if it shows up twice. I can't see it.
Reply
Brian Cockburn
3/9/2023 09:47:30 am
This should be fine unless the AHJ says otherwise. The Fire Department (along with police) would block the road while the fire is dealt with.
Reply
Anthony
3/14/2023 09:02:30 am
This.
Reply
JH beat me to it and has it exactly correct.
Reply
JH
3/9/2023 12:25:35 pm
Very true. We recently had a project that, even though there was an existing hydrant within the specified distances, using it under normal circumstances would have paralyzed fireground operations and impeded occupant evacuation as well as blocked ingress/egress from neighboring business. A new hydrant was ultimately installed to serve the new project.
Reply
Alex
3/16/2023 06:15:39 am
This is one of the situations where it’s allowed, but if possible, I would avoid it.
Reply
James Art, FPE
4/4/2023 12:03:59 pm
30,000 vehicles per day- per NFPA 1. THANKS!
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |