I have a K14 ESFR system in a tall building; 45-ft peak and 35-ft eaves, that was hit by the changes in NFPA 13 and there is now a recommendation to upgrade protection to K25 ESFR sprinklers due to the roof height.
The current design is a very strong 12 K14 @ 90 psi and the storage is low at 16-ft of palletized Class III and IV goods. Based on the current storage arrangement, 2022 NFPA 13 allows for either K25 ESFR system or a CDMA design of .64/2,000 using ordinary temperature sprinklers. Is is permissible to recalculate ESFR systems with a CDMA design? If so, is there any specific mention or directive in code? I am not a designer but back of napkin math indicates I have a 1.33 gpm/sqft. density over the first 1,200 sqft based on the ESFR design and probably a .80/2,000. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
12/21/2023 07:07:31 am
No its not acceptable to use ESFR in CMDA design. The problem is the different listing of the head. You can only use ESFR sprinklers in ESFR design.
Reply
Patrick
12/22/2023 10:40:20 am
Let me simplify the point of the question:
Reply
Franck
12/21/2023 08:09:29 am
Answer is simple : no !
Reply
Glenn Berger
12/21/2023 08:10:31 am
Anthony statement is spot on. Do not mix specific calculation methods that are applicable to specific specialize sprinklers.
Reply
Jes
12/21/2023 08:34:27 am
The short answer is "NO".
Reply
Dwight Havens
12/21/2023 09:22:37 am
"I have a K14 ESFR system in a tall building; 45-ft peak and 35-ft eaves, that was hit by the changes in NFPA 13 and there is now a recommendation to upgrade protection to K25 ESFR sprinklers due to the roof height.
Reply
Franck
12/21/2023 11:57:08 am
“but back of napkin math indicates I have a 1.33 gpm/sqft. density over the first 1,200 sqft based on the ESFR design and probably a .80/2,000”
Reply
Jay
12/22/2023 01:38:51 pm
Install a ceiling at the 35ft eave height and the sprinkler system won't need to be modified.
Reply
Jay
12/22/2023 01:43:51 pm
Clarification....obviously modifications will be needed to protect below the new ceiling, but the ESFR design of K14 heads can remain.
Reply
sean
12/31/2023 06:25:52 pm
I am not sure why we are mixing the versions of the standard?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |