I have a four-story hotel project to design that has bathrooms in the guest suites. These bathrooms measure out to 55.4 sqft per the architectural drawings of the bathrooms.
I am getting pushback from individuals as I don't feel this complies with NFPA 13-2016 Section 8.15.8.1.1's exception, and therefore it would require sprinklers. I interpret the 55 sqft threshold as 55.00 sqft, or am I interpreting this incorrectly and should allow sprinklers to be omitted as long as the square footage does not break into the 56-sqft threshold? The exception also states 5.1 square meters, which converts to 54.89 sqft, which to me, reinforces my 55.00 sqft threshold. What are your thoughts and feedback? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
26 Comments
Anthony
1/10/2022 07:38:00 am
Code is code, it is the law.
Reply
Jim
1/10/2022 11:02:18 am
It's not the law.
Reply
sean
1/10/2022 01:30:39 pm
his intent is correct.
Alex
1/10/2022 08:06:26 am
I agree with Anthony. This is one of many cases that arise where people look to stretch the code "just this one time". Sadly, if you give way here, next time they will look for the heads to be just 8' off the wall.
Reply
Jesse
1/10/2022 08:09:39 am
2016 NFPA 13R says sprinklers SHALL not be required in bathrooms where the bathroom area does not exceed 55-sq. ft.
Reply
Eric D.
1/10/2022 08:10:21 am
So as an AHJ and plan reviewer, 55 is 55. If it breaks the 55 SF mark (55.001), then sprinklers are required. Look at the past few days where sprinklers were not installed in buildings in Philly and NYC...high loss of life. If the architect wants to redesign the bathroom and reduce the SF to under 55 (as printed in black and white in the code/standard), then that is up to them. But if they leave it over 55 SF, then sprinklers must be dropped in to comply with the requirements.
Reply
Wes
1/10/2022 08:15:49 am
Just my opinion, but I think this is somewhat sloppy work by the architect.
Reply
Wes
1/10/2022 08:17:00 am
Also, it's Monday morning and I really should finish my coffee before getting asked about cutting corners...
Reply
Brian Willis Spurrell
1/10/2022 08:24:48 am
Codes are written and adopted as minimum requirements key word being minimum. In Canada the National Building Code does not allow the omission of any room on the top floor.
Reply
Todd Wyatt
1/10/2022 08:27:28 am
A hotel is classified by the IBC as a Group R-1 Residential occupancy classification. Per 903.2.8 Group R, "an automatic sprinkler system installed in accordance with 903.3 shall be provided throughout all buildings with a Group R fire area." 903.3.1.1.2 Bathrooms lists an exception to sprinklers in Group R bathrooms "that do not exceed 55 square feet in area ... provided the walls and ceilings ... are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating."
Reply
sean
1/11/2022 04:26:23 pm
NFPA 13R additionally can only be used if the area increase for sprinklers has not been used.
Reply
Glenn Berger
1/10/2022 08:36:09 am
Double check the area of the bathrooms with respect to face of finished walls. If still greater than 55 feet, then sprinklers are required.
Reply
Matthew Willis
1/10/2022 08:48:11 am
Also,
Reply
Joe F.
1/10/2022 10:45:15 am
I agree with Wes above, don't cut it so close. Even if the bathrooms are designed as 55 sq. ft. when the bathrooms are physically framed it is inevitable that some of the bathrooms grow in size in inch or two due to framing errors, and you will end up with an unsprinklered bathroom that is >55 Sq. Ft. There needs to be room for error. Arch should design the bathrooms to 54 Sq. Ft. or less if they want to eleminate sprinklers.
Reply
DS
1/10/2022 12:30:29 pm
For all of those stating to follow the letter of the code (which I do as well), the requirement is for bathrooms inside dwelling units exceeding or greater than 55 sf.
Reply
sean
1/10/2022 01:34:31 pm
I don't know your role or the role of the other individuals but this is a good time to document it.
Reply
Jack G
1/10/2022 03:56:39 pm
Be careful. There is always a note on all architectural set if drawings , that the dimensions are within 1,5 inches and can vary.
Reply
Jon N
1/10/2022 08:24:55 pm
I have read the previous posts and I must admit that, as an AHJ, I am torn on this. Yes; 55 ft. is 55 ft. but don't forget that the administrative chapters of virtually every code requires "reasonable" enforcement or states that the code is intended to provide a reasonable level of fire (or life) safety.
Reply
Jessica Lutz
1/11/2022 10:19:51 am
55 sqft is the limit...period.
Reply
Munny Khan
1/11/2022 01:20:23 pm
I would definitely err on the side of caution and add a head anyways.
Reply
Chris Hall
1/11/2022 02:46:33 pm
I pulled the SQFT from an enlarged bathroom plan with dimensions. I feel like they should be sprinkled as I interpret it as 55.00sqft, but at this point I feel like it is really splitting hairs. I told our other designer to proceed with heads in the bathroom unless the architect/owner can come back and tell us that the bathrooms will all be under 55sqft. I know for a fact there are some hotels in this area that have bathrooms over 55sqft that aren't sprinkled. But I had nothing to do with them, and skirting code isn't for me. In a way to add to the "splitting hairs" when we pull the sqft with Autosprink on the CAD drawings it shows it as 55sqft.
Reply
Jay
1/11/2022 04:28:37 pm
NFPA 13 speaks to not using a level of precision greater than intended.
Reply
Anonymoose
1/11/2022 06:41:15 pm
55 SF = 2 significant digits
Reply
Eric Young
1/12/2022 11:17:38 am
Let's say a fitter installs sprinklers 10 feet apart. Going back, we measure and find one head is actually 10.042 feet from the next. The pipe was not screwed in as far as the others. Is it over-spaced? Well, yes! Time to re-cut that pipe? No.
Reply
Chris Hall
1/12/2022 09:04:00 pm
And those are good points, and part of why I sent the question in. The significant number comment intrigued me because that’s a good point, and made me think about how the .4sqft overage technically would round down if you are going off of the figure as a whole number.
Reply
sean
1/12/2022 09:50:44 pm
while eric's thought experiment is nice, I don't think it holds up. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |