NFPA 13, Section 8.2.6.3.1 states that the compressed air supply shall be from a source available at all times.
Does this mean that it has to have a battery backup, or an inverter, if there is no generator? Thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Jesse
9/6/2022 08:02:53 am
No battery backup required but it does require a dedicated circuit.
Reply
JI
9/6/2022 08:09:45 am
I agree with Jesse, but as an aside, a compressor with a tank mounted on it should be able to provide adequate air pressure for a short power outage.
Reply
Alex
9/6/2022 08:12:26 am
Hi,
Reply
Brian Gerdwagen
9/6/2022 08:38:43 am
The reason it does not need backup power is the system is fail-safe. If there is a long period of power failure, your dry system will become a wet system.
Reply
Glenn Berger
9/6/2022 10:18:26 am
The requirement is a reliable source (always available). Depending on the type of facility and the how the power supply is configured will determine how the requirement can be met. You question did not specify if your project contained dry-pipe systems or pre-action systems.
Reply
Ken Thackery
9/6/2022 10:26:32 am
Dedicated circuit only. Power supply is not in our scope.
Reply
schulman
9/8/2022 08:38:08 am
i've done jobs with available emergency circuits that we used for the compressor as we were protecting sensitive equipment so we did not want the "fail safe" feature filling the pipes with water unless there was actual fire-caused sprinkler head release
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |