Is an access panel or access door required for sprinklers that are installed in a concealed space?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
10/25/2021 07:37:40 am
NFPA 13-19'-9.3.9.3 Sprinkler Access - Access shall be provided to all sprinklers for inspection, testing, and maintenance.
Reply
TC
10/27/2021 09:41:26 am
NFPA 13 2019- 9.3.9.3 is a subsection of 9.3.9 Duct Protection- this requirement for access panel is for Duct sprinklers.
Reply
Alex
10/25/2021 07:58:56 am
Hi Anonymous,
Reply
Dave
10/25/2021 10:18:44 am
Since 8.15.13.3 (2016) is a subsection of 8.15.13, that is only for duct sprinklers. There is no requirement in NFPA 13 or 25 for access panels for concealed spaces. Although I have seen owners wish to have them provided, and I have seen military specs requiring them.
Reply
Alex
10/25/2021 01:21:04 pm
Hi Dave,
Jack G
10/25/2021 08:21:30 am
Back in the day, 51 years ago, architects would show access panels in hard ceilings next to where designers would place the sprinkler heads for , specifically for access, repair.
Reply
Todd Wyatt
10/25/2021 09:34:19 am
The Specifications (e.g. 083113 Access Doors and Frames) instruct the Contractor to "Verify access door locations and sizes provide required maintenance access to installed building services components." and "Install access doors and panels permitting access to service valves, traps, dampers, cleanouts, and other mechanical, electrical and conveyor control items concealed in walls and partitions, and concealed above gypsum board and plaster ceilings."
Reply
Jesse
10/25/2021 10:26:07 am
There is a lot of debate within the AHJs in my area about this.
Reply
Dave
10/25/2021 11:33:44 am
NFPA #13:
Reply
DON BERRY
10/11/2022 01:30:33 pm
If a concealed space requires sprinklers (like a wood truss attic),is not inspected, how do you know if the fire protection for the attic meets code? NFPA 13 requires all heads to be inspected.
Reply
Brennan
7/17/2023 05:40:37 pm
You would get an inspection signed off by the ahj before they installed sheet rock on the underside of the trusses.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |