We have a storage building that is non-sprinklered, it only has fire alarm. The ceiling height in some areas of the building with storage of tires is up to 10-ft in height, and others up to 15-ft in height.
How many tires can be stored? Is there a limit to the amount of storage? Does storing on tread or on side matter? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
1/16/2024 08:08:24 am
Need to know the square footage of the facility and what are the applicable codes the govern in your jurisdiction in order to provide a knowledgeable response.
Reply
Pete H
1/16/2024 08:29:07 am
Agree with Glenn, this is going to depend on ICC and your local jurisdictions codes and ordinances.
Reply
Jesse
1/16/2024 10:12:38 am
So much more info is needed here.
Reply
Conrad
1/16/2024 12:00:24 pm
If reviewing this as new construction, I would ask for storage commodity class, storage layout with max height, and have that height permanently marked on the walls or similar. You may need a qualified engineer with fire protection background to design this.
Reply
In NC tire storage requires a sprinkler when the area of storage exceeds 20,00 cubic ft. Because we also consider tire storage a High Hazard Commodity when stored 6 ft. or higher, our Chapter 32 for High Piled Combustible Storage kicks in and places further restrictions on pile size, fire alarm, smoke & heat removal, building access and pile dimension's. Not sure where you are located or what code you use but hopefully this helps
Reply
Todd E Wyatt
1/22/2024 05:06:17 pm
Buildings that include the “bulk storage of tires” (storage >20000 SF) is classified as a Group S-1 Moderate-hazard Storage.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |