Have a current project that is stalled due to water supply conditions. A water flow test was not conducted early in the project.
Options have been presented to the other responsible parties for consideration, however a particular party has rebutted with “Where does it say you can not go below a certain water pressure?” The existing water supply would be taken down to 6 psi and the questioning party wants documentation on the standards of the lowest psi a water supply needs or should not drop below. Can anyone provide or give direction on finding information regarding water supply requirements or standards which address minimum water supply requirements? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Rusty Scott
7/22/2019 10:21:52 am
Typically AHJ requires the water system to not be drawn past 20 psi. A low suction control valve is often used to control this when you are close. An article that I think helps under stand the idea is below. I believe it is the water system's company provider who is the one that makes the final determination on what the limiting psi is, I would check with them. I think most would agree that the FP industry standard is 20 psi in the minimum. Sounds like you need a water storage tank/vault.
Reply
Douglas E. Colter
7/22/2019 10:34:18 am
This is one of those questions you have to scratch your head on, because they should not be asking it, and it is not necessarily in the building codes. And Uh, Duh, why are they asking it? The building systems have to work!!!
Reply
James Phifer
7/22/2019 11:06:22 am
From NFPA 24: Appendix C;
Reply
Mike
7/22/2019 03:09:50 pm
Taken down to 6 psi at your required flow?
Reply
John Kupcha
7/22/2019 04:56:12 pm
Water Pressure: The New York State Department of Health standard indicates that normal water pressure in the distribution system should be approximately 60 to 80 psi and not less than 35 psi while maintaining a minimum pressure of 20 psi under all conditions of flow.
Reply
Laura
7/23/2019 10:17:46 am
NFPA 1, Table 18.4.5.2.1, has requirements for fire flow, and these are to be available at 20 psi per the dagger footnote. See Section 18.4 for applicable reductions based on your building. There is the possibility that the required fire flow is less than your sprinkler system demand, but it is a straightforward reference to 20 psi that may be helpful to you.
Reply
Ed Berkel
8/28/2019 03:22:22 pm
I think most fire departments utilize the 20 psi; however, it is my understanding from our water purveyor that the Clean Water Act doesn't allow them to design below 35 psi
Reply