This feels like a silly question, but we have high-piled, non-combustible storage, with open-grate or solid level single/double row permanent racks with Extra Hazard Group 2 overhead system.
I'm trying to identify the actual code verbiage that says nothing is required from an code/NFPA standpoint. The product is metallic car parts with no added materials, just exposed solid metal, no plastic gaskets or spacers, etc. The 2015 IFC is the highest code in my jurisdiction, so starting with that, Chapter 32 is for High-Piled "Combustible" Storage and provides no avenue for code justification. NFPA 13-2013 defines "Noncombustible Material & Automotive Components on Portable Racks" but also gives no criteria for non-combustible storage. FM Global Data Sheet 8-1 actually lists noncombustible as a commodity classification, unlike NFPA 13, but does not provide a criteria stating no coverage. Is this just the simple scenario where code or NFPA standards don't list a requirement or criteria because it just doesn't require anything? Again I feel like it's a silly question given the commodity but I believe the only rules to follow would be obstruction rules and distance from deflector to storage. Thoughts? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Matt
4/3/2023 08:14:25 am
First thing, classify the occupancy using the adopted IBC (Maybe Group S-2).
Reply
Todd E Wyatt
4/3/2023 10:35:16 am
SUMMARY
Reply
Todd E Wyatt
4/3/2023 10:35:37 am
REFERENCES
Bobby V
4/3/2023 08:47:43 am
First off, l'm not sure what you mean by " nothing is required from an code/NFPA standpoint." Do you mean leave the existing OH2 as is, or are you trying to justify a sprinkler system is not required?
Reply
Dan Wilder
4/3/2023 08:53:49 am
So the commodity is non-combustible (Class I, maybe a II), what about the pallets? Reinforced plastic pallets would drive you into a Class III/IV automatically. standard plastic or wood pallets would push you to a Class II/III (again depending on where you start for the commodity itself). Anything about idle pallet storage within the racking as well?
Reply
Franck
4/3/2023 09:52:03 am
I saw your configuration sometimes in the automotive industry, as well as in steel plants.
Reply
Anthony
4/3/2023 11:14:57 am
This (good work Franck), Also check IBC for S-2 and F occupancy over 12K sqft requirements.
Reply
Jesse
4/3/2023 10:14:06 am
Linke Frank, I've seen this too in automotive mfg. You stated no packaging, but I'm wondering if there are pallets.
Reply
Sundance Bob
4/3/2023 10:55:39 am
Non-combustible is Class 1 commodities per NFPA-13.
Reply
Todd E Wyatt
4/3/2023 03:15:56 pm
“HIGH-PILED” is referenced per the scoping Code (e.g. 2021 IBC) (9) time in “Chapter 9 Fire Protection and Life Safety Systems” :
Reply
Franck
4/4/2023 11:22:16 pm
Class I means something to burn, i.e. pallets or packaging.
Reply
8/4/2023 07:52:14 pm
I have a related situation.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |