NFPA 30 Figure 16.2.5 is used to determine if a material is viscous liquid or not. I am having an issue with a interpretation of the "Weight (percent flammable or combustible liquid)". Is this weight for the liquid only or the liquid plus the container? Example: Total package / container weight = 2.48 grams. The liquid inside is a Class III-A mixture that is 0.78 grams (31.5%). If I go with the entire package Figure 16.2.5 is applicable (less than 50%), but if I am just looking at percent of combustible liquids, all the liquid is combustible.
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Franck
7/28/2021 08:18:22 am
Liquid only.
Reply
Franck
7/28/2021 08:23:12 am
Note that this would be different for solid storage commodity, where we are looking for the % in weight or in volume for plastic to determine an overall class III, class IV or Group A plastic commodity. But solid fires do not behave the same way as liquid fires (pool fires, quick evaporation for rapid spread...).
Reply
Jesse
7/28/2021 09:14:43 am
I was about to type an explanation, then hit refresh. Franck covered it all
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |