This week I'm wrapping up some coverage of fire standpipe systems. In case you missed it, here are the recent articles on this topic thus far: An Introduction to Standpipes Addressing Egress & Clearances for Standpipe Hose Connections Standpipe Connection Location by Code Edition Whether a standpipe hose connection should be located on a floor-level landing or an intermediate-level landing has been a classic tactical and design discussion in the fire protection community. Defining Floor versus Intermediate Landings A main floor-level landing is the horizontal portion of a stairway where the stair risers stop and occupants can enter a floor level, leave a floor level, or turn to walk on the stair itself. Intermediate-level landings are the horizontal portion of a stairway where the stair risers top and occupants can turn to continue onto the stair. Defining floor-level versus intermediate-level landings. Landings offer a resting space when transcending stairs as well as limit the distance someone is likely to fall down a flight of stairs. Stairs that jog back and forth with landings offer some benefits. They help limit the building area dedicated to stairwells, they create a consistent door location on each floor, and they to help break up long stretches of stairs. Do hose locations matter? They do. Hose connection locations have implications on the tactical approach for firefighters, the ease of installation for contractors, the complexity of design for designers & engineers, and the cost implications for building owners. Standpipes at floor level landings offer a simpler overall installation with design benefits. Benefits of Connections at Floor-Level Landings Benefits to standpipe connections at floor-level landings include:
Crossing the stair with sprinkler feeds from combination sprinkler/standpipe risers on intermediate-level landings can create head-height issues or knee-knockers, depending upon the approach. Standpipe hose connections at main-level landings help avoid these issues.
Connections at intermediate level landing requires that designers and engineers account for the additional hose length needed just to cross the stair. Benefits of Connections at Intermediate-Level Landings With all the benefits to designers, installers, and overall simplicity, why would intermediate-level landings be considered? Mostly it’s about first responders and the tactical approach in firefighting. Connections at intermediate-level landings offer more tactical than design benefits. Benefits to intermediate-level connections include:
Conversations with AHJs Regardless of approach, code stipulates a prescribed method but allows the AHJ the latitude to shift the landing location as he or she sees fit. Like other nuances of suppression design, it can be very beneficial to make the call and confirm an approach well before submitting plans. Other Considerations Here are a few important considerations that accompany standpipe design:
Don’t get these articles sent to you weekly? Subscribe here and join us in creating better fire protection.
Robert Shieh
7/12/2019 03:48:10 pm
Is there a reasoning why we only need 1 standpipe connection on the roof? Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
May 2024
|