How can we prevent the formation of algae or microorganisms in water storage tanks for fire protection due to the water being stagnant?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
I'm putting together design-build requirements for a new single-story construction building. The flow test pressure is borderline in my opinion so I'll be calling for a fire pump.
When is a water storage tank required with a pump? I don't think the system needs one, but I just want to be sure. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Is it permissible to consider the refill supply for a water storage tank when sizing the tank?
The supply would come in above 20 psi. Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe NFPA 22, 2018 Edition regarding filling requirement and duration -
Section 4.2.1.4. states "The water supply shall be capable of filling the minimum required fire protection volume within the tank in a maximum of 8 hours" and at the same time Section 14.4.3 states "The tank shall be kept filled, and the water level shall never be more than 4 in. (102 mm) below the designated fire service level." If I understand correctly, as soon as the water goes below 4-inches from the normal filled level in the tank (HHL), the makeup water supply should be starting to replenish and the pipe sizes should be provided in such a way that the tank can be filled within 8-hours. In a fire, as the water is going down, the tank will always start full. What is the case where the tank would be emptied out (except maintenance) and need to be refilled within 8-hours? What if we store water in two tanks to allow maintenance - would we not need to meet this 8-hour requirement? I'm unsure of how these two requirements work together. Appreciate any feedback. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe I’m working in the construction of 4-star hotel. The water storage tank is underground made from concrete and the pump room is located above the water tank. The designer specified the fire pumps to be vertical split-case type! In order to follow code, I proposed to install vertical turbine pumps instead of the specified vertical-split case.
The supervisor Engineer is insisting to follow the specification of the fire pump and pushing me to create an underground pump room in order to install the specified pump set. Any recommendations to avoid this directive? I have a bad flooding experiences with this this type of subgrade pump rooms. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe |