The 2018 IBC, Section 1009.7 for Exterior Area for Assisted Rescue (EAAR) requires exterior walls within 10 feet to be rated 1-hour for exposure to fire from the inside.
When a window is located within 10 feet of the EAAR, can it be protected with a window sprinkler system? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
10/10/2024 06:46:42 am
As long as it is acceptable to the AHJ, you use the TYCO model WS, as long as the EAAR falls into:
Reply
Jesse
10/10/2024 08:08:42 am
Generally, yes as long as the AHJ accepts it. Another suitable alternative may be fire rated glass. That's porbably more expensive than window AS protection though
Reply
Todd E Wyatt
10/10/2024 08:45:19 am
See “IBC-2021 705.8.2 Protected Openings – Exception” below:
Reply
Jack G
10/10/2024 10:51:05 am
Anything bigger than 10x 10 in an exit stair or doors requires sprinkler protection. ( if stair is near unprotected walls)
Reply
David Toshio Williams
10/10/2024 11:10:44 am
The listing requirements for window sprinklers can be restrictive as far as architectural character. So certainly have a discussion with the architect as far as allowable size/stiles/mullions... for those reasons, fire rated glass maybe preferable. (Although the frames can be ugly too).
Reply
Glenn Berger
10/10/2024 11:48:50 am
If the window falls within a required rated wall, then the window needs to be protected to the same acceptable level. The fact that you have an AOR is just extra information.
Reply