Operationally, why would a fire department with a 1,500 gpm pump on a fire engine connect to a building FDC that has a 1,750 gpm pump?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Jon N
1/1/2025 08:26:52 am
Operationally, fire departments have a higher comfort level with their own apparatus' pumps than with stationary fire pumps inside a building:
Reply
Ron F
1/27/2025 10:36:52 pm
As a former career Fire Service Officier this is the answer. SOP was to connect to FDC and supply at starting psi of 130
Reply
Franck
1/1/2025 09:09:43 am
1. if the pump fails or is impaired
Reply
Chad
1/1/2025 09:45:24 am
As John said…. Murphys Law. Pumps fail.
Reply
Andrew
1/1/2025 12:41:25 pm
It does seems counterintuitive at first, but something to consider is if a low rise fire (>150 PSI) is at a point where the sprinklers have failed to gain control before the FD pulled up, it's likely that either something in the system failed, or it was started catastrophically and is simply beyond the design of the building's system. Setting any system up with a 1500 gpm @ 150 psi pump is just a cheap insurance policy anyway and almost guaranteed to have a superior curve to whatever's in the building
Reply
Dan Wilder
1/1/2025 05:31:17 pm
Resource deployment for any SaR and internal fire attack will rely on a stable, controllable, and monitored water supply. Placing someone into the building to monitor if a fire pump is ON or OFF (if it's even accessible from the exterior safely) without any means to change variables like pressure is a waste and adds an additional point to monitor for Incident Command, notwithstanding the potential need to change out SCBA and personnel further adding to a complex situation.
Reply
Jack G
1/1/2025 05:32:08 pm
From what I ve witnessed, one of the fire departments initial moves is to shut off the electric to the building, whether it’s pulling the meter on a house or shutting down the power to a high rise, to avoid electrocutions.
Reply