I have an NFPA 13D system covering an ADA house that has two pumps in the basement. I am struggling to understand why the two pumps were installed in parallel.
Would this just be to increase Total Dynamic Head (TDH)? Why would you need to increase TDH on a residential system? Basically, the customer wants the pumps replaced with new ones because they're old, and I guess what my question really boils down to is what info do I need to figure out to replace these pumps with the correct size pump(s) to satisfy system demand? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Brett
2/24/2026 06:39:25 am
Pumps in parallel don't increase the TDH beyond what one pump can do, but they do increase the total flow that the system can output. Pumps in series increase pressure and pumps in parallel increase flow. It's also possible that the original installation put two pumps in parallel simply for redundancy as an N+1 configuration.
Reply
Chad
2/24/2026 08:06:53 am
Have you tried running a calc estimating the pipe?
Reply
Richard W Mercer
2/24/2026 08:25:18 am
I'm not familiar with the Term ADA House, but the base code that applies may have some answers. For Example, the Life Safety Code has some additional requirements, when NFPA 13D designed systems are used in Residential Board & Care Facilities.
Reply
Jack G
2/24/2026 08:45:58 am
An nfpa 13 d system uses pumps in parallel primarily to increase total water flow (gpm) while maintaining consistent pressure ensuring reliable coverage for larger homes.
Reply
Jon N
2/24/2026 08:50:37 am
Is it possible that this had nothing to do with hydraulics and/or water supply but that the maximum size of the pumps was limited by the electrical supply available and it could not handle a larger pump due to amperage or voltage?
Reply
Glenn Berger
2/24/2026 08:51:10 am
Concur with Brett on his pumps in parallel vs pumps in series explanation.
Reply
Justin Reid
2/24/2026 09:05:19 am
Like stated by others, pumps in parallel increase flow at the same pressure. Because you are limited by your supply line, this would not make sense in a small accessory dwelling unit application. So it is likely either redundant, or like was stated by others there was a limit on the electral service available to supply the pumps. They may have split the flow into two smaller HP pumps with likely staggered starts. Check the sequence of operations to determine if they both kick on or if one is truly redundant. Safest bet is to install like for like, but if you can make the system work on your own, you can always go that route. AHJ's usually will allow a like for like repair with little to no justification. If you go with a new arrangement, you will have to prove the entire system works. Good luck!
Reply
danefre
2/26/2026 11:20:10 am
ADA rules in your state might require tweaks, but they rarely affect residential fire pumps. I've heard of two tanks for 30-minute duration (vs. standard 10 min in NFPA 13D), but dual pumps is uncommon, NFPA 13D doesn't require redundancy unless there's a specific reason (e.g., well capacity or extra reliability).
Reply
Leave a Reply. |