Why Product Data Separate from Shop Drawings?

10/6/2026

8 Comments

 
Why Are We Still Separating Fire Alarm Equipment Submittals From the Shop Drawings?

I’m looking for input from the engineering community on something I continue to struggle with in the typical A/E submittal process.

On many projects, the fire alarm equipment/product data is submitted early, and the actual fire alarm shop drawings, calculations, riser, sequence of operations, interfaces, circuiting, and other system-design information follow later. This appears to be a long-established A/E practice, but I increasingly question what meaningful engineering review is supposed to occur at that first equipment-only step. With product data alone, I can determine that the proposed manufacturer is acceptable, that the equipment family generally complies with the specification, and that I do not see an obvious reason the contractor should be prevented from purchasing the equipment.

What I cannot legitimately determine is whether the equipment package is complete, properly sized, properly configured, or sufficient for the actual fire alarm system. Until I see the shop drawings and calculations, I do not know whether the contractor has provided the correct quantities and capacities of panels, power supplies, amplifiers, modules, network equipment, batteries, interfaces, survivability components, and everything else required to make the system work as intended. Because of this, I have actually revised my own fire alarm specifications to require the product data, shop drawings, calculations, sequence of operations, and associated system-design information to be submitted together as one coordinated system submittal. Yet I continue to see the industry separate them anyway. And that is part of what I am trying to understand.

Is there a real technical or contractual reason for doing this, or are we simply continuing a process because “that’s how we’ve always done it”?

I struggle with that mentality, particularly when the established administrative process does not appear to fit the way an engineered system actually needs to be reviewed. I recently had a situation that highlighted the problem. The proposed equipment itself was acceptable, but the overall submittal had to be formally rejected because the required shop drawings had not been provided. I specifically indicated that I had no objection to the proposed equipment, but because the official disposition was Rejected, the contractor would not release the equipment for purchase. That seems like a contradiction created by the process itself. I do not want to give an unconditional approval to an equipment package when I have not yet seen enough of the system design to support that approval.

At the same time, I do not want the contractor prevented from purchasing equipment that I have reviewed and have no technical objection to them procuring. What I would really like to be able to communicate is something along these lines: No objection to procurement of the proposed manufacturer and equipment. This review does not constitute acceptance of equipment quantities, capacities, configuration, system architecture, interfaces, calculations, or overall system completeness. Those items remain subject to review of the complete coordinated fire alarm shop-drawing submittal. There is also a separate review-time issue that compounds the problem.

On projects with a nominal two-week A/E submittal review period, the fire protection engineer may not actually receive the package until it has already passed through the subcontractor, electrical contractor, GC, and Architect. In practice, I may receive it with only two or three days remaining. For a complete fire alarm submittal containing drawings, calculations, product data, sequences, interfaces, and specification requirements, I also question how the industry expects a legitimate engineering review to occur under that compressed timeframe.

So the three questions I keep coming back to are:

1. Why are we still separating fire alarm equipment from the shop drawings, calculations, sequence, interfaces, and other system information needed to actually evaluate it?

2. How do we allow the contractor to purchase technically acceptable equipment without giving an engineering approval that the information submitted does not yet support?

3. How do we change the “this is how it’s always been done” process so the complete fire alarm system submittal can be submitted together—and the engineer is actually given enough time to perform a legitimate review?

​I would especially like to hear from people who know why this sequencing developed in the first place, but also from those who have successfully changed their specifications, contracts, routing, or submittal schedules to make a complete coordinated review possible.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
10/6/2026 06:17:23 am

1) Timing and Space. We want to look at product data for budgeting as much as we do for evaluation. We want to do that before we pay someone to design the project. So submittals are filed before the shop drawing, this way if the design team takes issue with an item on the submittal: it is resolved before the shop drawing design. Also, it's minimum an extra page of drawings that the field techs don't need because they get copies of the tech specs and catalog cuts with the material shipments.

2) "I'm not going to tell you no, but I can't tell you yes either."

3) Oh we can't. Unless the people financing these jobs are massively changing their timeframes and schedules to just accept a lot of extra padding, they're going to want to rush something they can rush.

Reply
Dan Wilder
10/6/2026 08:09:32 am

1. Submittal of equipment of the equipment generally aligns with a design that is viable for submittal. If a Contractor only submits on strobes, but the design requires audio notification, that is an identifiable miss in the submittals. Once I get that approval, I still don't have an approval on the design so if purchasing occurs, the responsibility is still on me (see 2).

2. Approval of equipment isn't an open checkbook for purchase. I still have to confirm panels that can support the devices, batteries, interface requirements with BMS, devices that support the building (dB and candela appropriate selections).

3. Those timelines you noted above are based on everyone BUT the fire alarm contractor. You start with those entities first and to owner.

As a side note, if you did receive a 100% package and immediately rejected it due to Material Submittals being incorrect without any review of the actual design, isn't the current process saving a lot of rework already? This would likely create more issues for the contractor and you both.

My thoughts are construction has taken such a step backwards the last 20 years with the "just in time" financing. The owner is trying to save himself money by releasing/requesting tiered loan amounts to allow the site/civil to start but saves a month or two in interest by waiting for structure (or vice versa pending the market). Then wait a little longer and release electrical, maybe mechanical due to lead times. Somewhere down the line for us 5% and under subs, we get let loose and come into projects that are already built and are told to have submittals within 72 hours, shops within a week, and onsite in 3 weeks....oh ya, AHJ approvals take 1-3 months.

I had this issue recently with a project....we got brought on on a Monday for the GC kickoff (site, VDC, schedules...) the signoff for phase 1 of the construction was Tuesday (we got the BIM meeting notice forwarded to us after that gem dropped in the meeting). They wanted shops in 2 weeks (this is a TI/new construction within a 150K ft² ESFR warehouse with only half the as-builts and a laser & Matterport scan to reference prior to the onsite survey). Flow tests take 1-2 weeks (we cannot perform them in this AHJ), submittals take 6 weeks (maybe 4 pending the queue) and we have to draw and coordinate at the same time to maintain the construction schedule. Fix that timeline and I will happily give you 100% submittal packages as I will have time to make adjustments. If not, I will work to piece together every approval as available to avoid a complete redesign.

Reply
chad
10/6/2026 08:15:37 am

1- Its not taken seriously enough by owners, architects and AHJ's. We collectively need to hold a standard

2- Laziness and a lack of understanding. Also ineptitude, just because you are an EE or Arch that does not make you qualified to design or approve FA shop drawings, and that is clear in all 50 states licensing, but its not taken seriously enough


3- By requiring a minimum standard for qualifications for both the submitter and the engineer reviewing it. And the AHJ needs to understand this and enforce it, which is also a big problem.

NICET III/IV or FPE, or proper documented training and experience for other PE/Arch should be the standard, IMO


Reply
Brian Gerdwagen
10/6/2026 08:59:57 am

1. A number of right answers have been given. The separation allows us to verify that the products meet the spec before shop drawings are started. Many times a client will request a specific manufacturer only for the contractor to submit a different one. Do we fire the sub because they can't install the requested products?

2. They should not be buying anything until the shop drawings are approved. Regardless of equipment submittals.

3. Given my answers to the above, I do not see the problem with continuing the way we have always done it. The contractor is allowed to purchase anything they want at their own risk.

Reply
Jeff Ayers
10/6/2026 09:31:47 am

On 99% of the projects completed over the last 40 years, the FA and Sprinkler are Delegated Design.

The submittals are a peer review from the EOR only.

The approval is ultimately subject to the AHJ for code compliance, making the EOR review perfunctory at best.

Often the submittals from EOR come back as "reviewed" with very little comments, and rarely ever "Approved".

The EOR review is typically for Owner compliance needs, such as making sure the FA devices are not proprietary to one system and allow other components to be added from another manufacturer.

Reply
chad
10/6/2026 09:43:20 am

This is the problem.

Its delegate....to the the lowest bidder. If hey cannot properly do a submission its a mess, EORs will mark total junk "reviewed", its irrelevant

Responsibility needs to be clearly defined, and the contactor is on the hook when it is not, but they are often unable to competently. What this leads to is every AHJ making up a laundry list of special rules. Some states take the lead so its less disjointed but the core issue remains, there is no clear responsibly party and an over reliance on the AHJ as an SME, when often they are not.

The boilerplate cut and paste notes from delegation are seen as the buck being passed. And perhaps it is legally, but its still a mess and collectively we perpetuate it across the industry.

Reply
Jeff Ayers
10/6/2026 09:56:47 am

You are correct. The AHJ review and the EOR review is usually an overview only. They both end up stamping language that basically states "reviewed for general conformance" & "device types and locations must meet IFC"... or NFPA or whatever code the building is subject to.

Then at the end of the project, we are swapping out horn strobes with brighter candela, adding exit signs, adding pull stations etc. when the FM performs the final inspections.

Normally the AHJ only comments on where they want the annunciator and FACP and almost never comments on the devices submitted.

However, as a developer builder I know the key items to check for when I complete my product data and shop drawing review. Such as making sure the exterior devices are designed for 0` wet environments, making sure they have devices in enclosed courtyards, etc.

chad
10/6/2026 10:12:35 am

Another good point.... no one checks the details and then we are all waiting on rework. If we put the time in it initially, the final AHJ inspection should be easy and boring. I am critical on plan details like that, along with a proper I/O Matrix so we are not standing there waiting on the programmer to redo mapping.

But its not just on the AHJ, the EOR (or someone!) should be held to account for the major details on deferred shop/submittal drawings before they get to the AHJ for review.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT