Does anyone know the historical context of why a 90-minute door is permitted on a 2-hour barrier?
Why the 30-minute difference? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Todd E Wyatt
10/21/2024 08:16:47 am
From idighardware.com :
Reply
Todd E Wyatt
10/21/2024 09:22:01 am
That being said, some users (after the Certificate of Occupancy has been issued) of a room with (2) fire doors (FD) will sometimes place storage (e.g. file cabinets) in front of the "unused" FD which "voids" its fire-resistance rating (FRR) since it now has a higher fuel load in front of it.
Reply
Dan Wilder
10/21/2024 08:19:36 am
Can't speak to the history but when tested to NFPA 252
Reply
Greg
10/21/2024 08:21:43 am
....Could it be the hose stream portion of the Fire Door Test is included in the total duration of time and therefore the hourly rating is rounded up?
Reply
Chris Nelson
10/21/2024 08:56:11 am
This was my question. Thank you all! The limited fuel load makes sense!
Reply
Jack G
10/21/2024 10:21:12 pm
I agree with the above comments. Unless the fire door is unused, and allowed to be blocked off for storage —- as long as egress allows the reduction of exits—- 90 minutes is fine.
Reply
Mike Morey
10/24/2024 08:21:24 am
IBC Table 716.1(2) lists the door requirements relative to wall requirements, for what it's worth, including allowable glass sizes etc.