Why is there a drastic change for limiting an NFPA 13R sprinkler system from a four-story, maximum 60 feet height above grade plane in IBC 2018 to the maximum of the top floor being only 30 feet above fire department access in IBC 2021?
Here, we have many townhomes (R-3 group) that could easily comply with the 2018 edition of the IBC, but they will exceed the top floor 30-foot limit of the 2021 edition of IBC. Also, the 2024 IBC tries to fix the drastic change by providing an exception for Group R-2 buildings by raising the top floor height limit from 30 ft to 45 ft. That's great and all, but townhouses are still considered R-3 buildings and do not qualify for the exception. How would you proceed for a townhome with a top floor over 30 feet above fire department access? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
11/26/2024 06:51:00 am
If your jurisdiction has adopted 2021 IBC, and not 2024 edition: protect as per NFPA 13 instead of 13R.
Reply
Joe Mc
11/26/2024 08:17:01 am
If you wish you can watch the debate for any ICC code item at
Reply
Brian Gerdwagen
11/26/2024 08:28:14 am
You use a 13 system. Not a 13R.
Reply
Dan Wilder
11/26/2024 03:12:10 pm
The change was partially tied to the same height requirements as standpipes.905.3.1.
Reply
Conrad
12/5/2024 12:35:04 pm
NFSA page on this specific issue: https://nfsa.org/2022/12/15/nfpa-13r-and-the-international-building-code/#:~:text=30%20ft%20requirement%20inadvertently%20limited