Why Aren't Added Standpipe Flows Balanced?

6/19/2026

7 Comments

 
When adding flow of additional standpipes (vertical standpipes with a horizontal connecting main), the NFPA 14 handbook (NFPA 14 10.6.1.2.4) explicitly says that flows shall not be required to be balanced.

I get the logic of balancing the calc, and it's not terribly hard to do - but what's the difference?

Is not balancing the calculation more conservative?

Is it insignificant, and therefore doesn't really matter?

Why aren't we required to balance the calc by code?


Thanks in advance.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
6/19/2026 08:24:14 am

Good Friday question! The current/former fire fighters can better speak to a lot of below but in my searching...

Best I can provide looking into this is that the flow calculation is performance based to provide that the minimum flow and pressure is available at the flowing points because the actual flow and pressure requirements are unknown at those points. They are all independent of each other (the hose valves) and are not setup with any predetermined requirement (this hose valve supports these hose and nozzle types)...

Will a single 2½" nozzle be used with a wye and feed smaller 1½" - 1¾" attack line needs stream and fog capabilities separately? Not a clue... Will a single 2½" hose be used with a nozzle, likely not but there is a possibility (can't drag that around very well). Will they pull lines from separate hose valves to the same area to provide better coverage. Again, not a criteria we as designers are required to align with as we are just providing what seems to be the best overall approach to most of the responding department's needs.


Reply
NK
6/19/2026 08:56:47 am

The hose allowance for a fire sprinkler system in NFPA 13 is based on providing the fire department water for final extinguishment (assuming that the fire sprinkler system is controlling the fire like it's designed to).

The standpipe hose system demand in NFPA 14 is for manual firefighting operations which can either be in a non-sprinklered building, or in a sprinklered building where the sprinkler system control valve is closed for the fire department to manually intervene to extinguish the fire.

If everything works correctly, there really shouldn't be a situation where you have a fire sprinkler system fully activated over the entire remote AND a hose allowance for final extinguishment AND need an additional 1000gpm of water at 100psi for fire fighting operations. I'm not saying this always happens, but the codes and standards are based on everything working as designed, not incase things fail. If the expectation was that things were going to fail, it would be very hard to standardize anything.

Reply
Mark Harris
6/19/2026 09:06:46 am

Not sure if this is the question but if is about balancing flows for additional vertical standpipes (NFPA 14 not sprinklers NFPA 13) my interpretation is if it flows at hydraulically remote standpipe any closer less hydraulic demand standpipes or connections would provide more flow and or pressure. Like the worst case remote design area for a closed head fire sprinkler system.

Reply
Jose R Figueroa
6/19/2026 10:17:10 am

It is presumed that the fire protection system incorporates automatic sprinklers. These standpipes shall not be considered in the balance calculation for gridded or looped systems. Omitting the balancing of added standpipe flows (referencing NFPA 14, section 10.6.1.2.4) represents a deliberate and code-compliant simplification, which is generally more conservative for the supply piping and remains pragmatic due to the performance-based requirements of standpipe demands.

Reply
Mike Russell
6/19/2026 10:47:38 am

Without getting into the inherent differences between a sprinkler with a fixed k-factor and a hose valve, the intent of NFPA 14 is that you balance the pressure, but not the flow.

The code requires 250 gpm for each hose connection, starting with 100 psi at the remote connection. Depending on the edition, you add 250 gpm for each additional standpipe at the balanced pressure. Essentially, your remote connection should be discharging at 100 psi while each additional connection would have the same 250 gpm at slightly higher pressure.

Reply
Jack G
6/19/2026 01:52:44 pm

While it’s not recommended or referenced, I usually perform a “ supply calculation “ on the standpipe system with the 500 plus 250 plus 250 at the top ( 3 standpipe) and the program will calculate the pressure available at each valve. I then tweak it if needed, and then perform the required demand calculation.
I also initially do a supply calc on remote area calculations, tweak the pipe sizes if needed, then do the demand calculation.
In my opinion, the supply calc is what you are going to see , say when a remote area goes off( accuracy wise ) as it uses all the water.
In the past, when I do a demand calculation with the normal 10 psi safety factor, that 10 psi puts the demand over the curve ( doing a supply calc on the calculation with the safety factor)
Real life or “ demand?”

Reply
Jack G
6/19/2026 01:58:35 pm

I initially was in special hazards for anbout 7 years. Transformers
and deluge systems.
The goal was to “ let the pipe sizes “ regulate the flow to prevent sometimes massive overflows. If that occurs the sprinklers involved will not deliver the required density.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT